The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#49993 - 03/21/05 08:20 PM Panel located below water pipe?
944mike Offline
Junior Member

Registered: 11/14/01
Posts: 2
Loc: Hartford, CT
I need to have a breaker panel moved. The only feasable location is directly below a copper water pipe.

The panel will be located about 1ft below the pipe, and the feeder conduit will have to cross the water pipe at some point.

Is this allowed, or will i have to have the pipe moved as well?

By the way, this is an industrial application.


Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#49994 - 03/21/05 08:58 PM Re: Panel located below water pipe?
Celtic Offline

Registered: 02/26/05
Posts: 367
Loc: NJ
Check 110.26 Spaces About Electrical Equipment.:

- 110.26 (F) Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage.
Exception: Control equipment that by its very nature or because of other rules of the Code must be adjacent to or within sight of its operating machinery shall be permitted in those locations.

- 110.26 (F)(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (d).
- 110.26 (F)(1)(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
- 110.26 (F)(1)(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
(Above from 2002 NEC)
While the code states no foriegn equipment may be in the dedicated equipment space, I have worked on jobs where this space was violated in more ways than:
1 - a humongous expansion joint which cut diagonally across 2 seperate 4000A switch gears

2 - Drain pipes (from rooftop and businesses located on the floor above) located directly above load centers/panelboards/distribution panels

3 - Water lines (supply and sprinkler systems) located directly over LC/PB/DP and SGs.

The soloution was to put in a metal drip tray. I did NOT agree with this solution as the drip trays did not have any provisions to drain the tray. The AHJs allowed the engi's "solution".

On a much smaller job (200A resi. service upgrade), the LC was relocated directly under the homes water supply line. The simple solution was to relocate the water line out of the way.

[This message has been edited by Celtic (edited 03-21-2005).]
~~ CELTIC ~~
...-= NJ =-...


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals