#49756 - 03/15/05 04:50 AM bonding sprinkler main
jsherrard Offline
Member
Registered: 07/10/04
Posts: 19
I have a 4" metal sprinkler main entering a building under construction. It needs to be connected to the grounding electrode system with a 2/0 conductor. None of the catalogs I have show a grounding clamp of that size. The flange bolts on the sprinkler main are a much larger diameter than the mounting hole on a 2/0 lug. Any suggestions as to other methods of attaching the 2/0 conductor?
Top
Work Gear for Electricians and the Trades
#49757 - 03/15/05 05:24 AM Re: bonding sprinkler main
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
There must be some test ports, gauge ports, and other smaller pipes branching off of the main, no?

Just attach to one of these with an appropriate clamp, making sure that there is a solid metallic path back to the main pipe.
Top
#49758 - 03/15/05 02:50 PM Re: bonding sprinkler main
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
There are several manufacturers of pipe clamps for larger sizes. Try the Greaves G1 Series (800-243-1130, sorry, I don't have a web address for them).

I have used ILSCO in the past, prices were very reasonable. http://ebusiness.ilsco.com/webapp/wcs/st...p;categoryId=77

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#49759 - 03/16/05 03:14 AM Re: bonding sprinkler main
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Jsherrard,
I'd ask the guys that installed the pipework.
We use the same sized pipes here and we use the same sized clamps as the installers to bond our pipes.
Just make sure that there is good metallic contact ie: Low Resistance.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals