The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#49479 - 03/07/05 03:50 PM derating
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
Sorry to be so dumb here, but I'm trying to figure out the derating in some circuits I will be pulling. Been a long time since I had to derate. I'll be having 9 current carrying conductors in 1 conduit. The total load on 1 circuit will be 49.38 amps. ( 3 phase ). Since I would normally use # 6 wire using the 60 degree table which is good for 55 amps, do I take 70% of the 55 amps, which gives me 38.5 amps? If so, then even if I use #4 wire, which is good for 70 amps, then that still will not be quiet enough to make the 49.38 amps needed, unless I can drop the .38 amps. But then again, if I can verify the terminals good enough for 75 degree wire, then I can go by the 75 degree table. But these machines are so old, I doubt I'll be able to verify that, since there is not a label to go by. I wonder if anyone could give me some input on this? The other two circuits will both be 26.3 amps. apiece. (3 phase also) thanks again

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#49480 - 03/07/05 04:14 PM Re: derating
Scott35 Offline

Broom Pusher and

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA

Here's some numbers for your derating situation:

If you use THHN insulation, then:

    [*] 9 # 6 THHN cu derated = 52.5 Amps,

    [*] 9 # 4 THHN cu derated = 66.5 Amps.

If you use THWN or THW insulation, then:

    [*] 9 # 6 THHN cu derated = 45.5 Amps,

    [*] 9 # 4 THHN cu derated = 59.5 Amps.

Hope this is helpful.

Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#49481 - 03/07/05 04:44 PM Re: derating
Electric Eagle Offline

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Sparky, the key thing to remember when detrating is to start in the column of the wire insulation and conductor type (cu/al). So for THHN or THWN-2, take the 90 degree column and derate based on the number of conductors. You then use that number as your maximum or the 60 degree column, whichever is less. Clear as mud?

#49482 - 03/07/05 05:00 PM Re: derating
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
Gee thanks guys, it's coming back now. I was using the 60 degree column for the derating on my thhn wire, makes a lot of difference. It gets "cloudy" sometimes when you don't use it on a regular basis don't mean to sound so dumb sometimes, life just gets to going too fast sometimes and I don't seem to have time to "sort" it out.... Thanks again for the help.. Steve