Doing a job wiring an unattached residential garage. I have to run the 100 amp subpanel feeders through the attic then down the outside wall to a underground trench then to the garage. Would like to run 2/3 NM through the attic but then when I get to the UG trench, I don't want to have to change to #2 THHN just to go through the ridgid pipe underground, that will require a splice. Can I run the 2/3 NM through the ridgid pipe?. Or I could run #2 THHN through flex in the attic then convert to emt down the wall, then to ridgid underground.
Any suggestions?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#49387 - 03/06/05 01:53 AM Re: Subpanel - Garage - THHN/NM
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Conduit underground is considered a wet location...
Romex is not allowed in a wet location...
Change over to pipe with thhn/thwn conductors...

shortcircuit
Top
#49388 - 03/06/05 01:25 PM Re: Subpanel - Garage - THHN/NM
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
With an emphasis on thwn
Top
#49389 - 03/06/05 06:24 PM Re: Subpanel - Garage - THHN/NM
George Offline
Member
Registered: 02/23/02
Posts: 380
t is hard to find THHN that is not rated THWN
Top
#49390 - 03/06/05 06:59 PM Re: Subpanel - Garage - THHN/NM
bucketman Offline
Member
Registered: 10/31/04
Posts: 71
Loc: vancouver WA, USA.
go pipe the hole way.
Top
#49391 - 03/06/05 08:51 PM Re: Subpanel - Garage - THHN/NM
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I agree with bucketman. You could use smurf in the attic and LB into RNC when you go outside if running the pipe in the attic is a problem.
_________________________
Greg Fretwell
Top
#49392 - 03/06/05 10:05 PM Re: Subpanel - Garage - THHN/NM
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Ya I agree, Prob the best way to go, I'll run pipe all the way.
Thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#49393 - 03/07/05 01:58 AM Re: Subpanel - Garage - THHN/NM
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
aldav53...Jus noticed your in Arizona...gets real hot up there in those attics out there.

Be sure to apply the ambient temperature correction factors for the wiring up in that there attic. You could use a correction factor that would cut the ampacity of the wiring by 50%

Find this info below table 310.16 NEC...

You would be better off to run underground to that garage.

shortcircuit
Top
#49394 - 03/07/05 03:04 AM Re: Subpanel - Garage - THHN/NM
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
"t is hard to find THHN that is not rated THWN"

Yes, As a matter of fact, I don't remember ever seeing any. You can bet, though, as soon as we say THHN is OK, that there will be some showing up for the first time. Accuracy is important, George
Top
#49395 - 03/07/05 09:40 PM Re: Subpanel - Garage - THHN/NM
aldav53 Offline
Member
Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
shortcircuit,
Have to run through the attic then down to the trench. Yes it is hot in attics here. I may have to go larger than #2 for 100 amps.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (HotLine1), 97 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals