The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 170 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#49386 - 03/06/05 01:26 AM Subpanel - Garage - THHN/NM
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Doing a job wiring an unattached residential garage. I have to run the 100 amp subpanel feeders through the attic then down the outside wall to a underground trench then to the garage. Would like to run 2/3 NM through the attic but then when I get to the UG trench, I don't want to have to change to #2 THHN just to go through the ridgid pipe underground, that will require a splice. Can I run the 2/3 NM through the ridgid pipe?. Or I could run #2 THHN through flex in the attic then convert to emt down the wall, then to ridgid underground.
Any suggestions?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#49387 - 03/06/05 01:53 AM Re: Subpanel - Garage - THHN/NM
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Conduit underground is considered a wet location...
Romex is not allowed in a wet location...
Change over to pipe with thhn/thwn conductors...

shortcircuit

Top
#49388 - 03/06/05 01:25 PM Re: Subpanel - Garage - THHN/NM
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
With an emphasis on thwn

Top
#49389 - 03/06/05 06:24 PM Re: Subpanel - Garage - THHN/NM
George Offline
Member

Registered: 02/23/02
Posts: 380
t is hard to find THHN that is not rated THWN

Top
#49390 - 03/06/05 06:59 PM Re: Subpanel - Garage - THHN/NM
bucketman Offline
Member

Registered: 10/31/04
Posts: 71
Loc: vancouver WA, USA.
go pipe the hole way.

Top
#49391 - 03/06/05 08:51 PM Re: Subpanel - Garage - THHN/NM
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I agree with bucketman. You could use smurf in the attic and LB into RNC when you go outside if running the pipe in the attic is a problem.
_________________________
Greg Fretwell

Top
#49392 - 03/06/05 10:05 PM Re: Subpanel - Garage - THHN/NM
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Ya I agree, Prob the best way to go, I'll run pipe all the way.
Thanks,
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#49393 - 03/07/05 01:58 AM Re: Subpanel - Garage - THHN/NM
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
aldav53...Jus noticed your in Arizona...gets real hot up there in those attics out there.

Be sure to apply the ambient temperature correction factors for the wiring up in that there attic. You could use a correction factor that would cut the ampacity of the wiring by 50%

Find this info below table 310.16 NEC...

You would be better off to run underground to that garage.

shortcircuit

Top
#49394 - 03/07/05 03:04 AM Re: Subpanel - Garage - THHN/NM
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
"t is hard to find THHN that is not rated THWN"

Yes, As a matter of fact, I don't remember ever seeing any. You can bet, though, as soon as we say THHN is OK, that there will be some showing up for the first time. Accuracy is important, George

Top
#49395 - 03/07/05 09:40 PM Re: Subpanel - Garage - THHN/NM
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
shortcircuit,
Have to run through the attic then down to the trench. Yes it is hot in attics here. I may have to go larger than #2 for 100 amps.
_________________________