The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 9
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#49367 - 03/04/05 07:43 PM bonding electrodes, separate buildings(common area circuits
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
given: 2 separate buildings , by use of a firewall, each building as its own service. ( common area branch circuits suppiled from one of the services is used to supply secuity lighting for both buildings) Should the electrodes from each service be bonded together to stablize any difference in potential ? What code section requires the electrode to be bonded in this case ?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#49368 - 03/04/05 09:17 PM Re: bonding electrodes, separate buildings(common area circuits
hbiss Offline
Member

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Nothing requires them to be bonded together if they are truly separate in separate buildings. This is not the case though, there are common area circuits serving both buildings from one of the services. Also, are there two separate water services from the street (or one that splits?) and do they require bonding? Are the meters and any disconnects next to each other?

-Hal
_________________________
www.myphonetechs.com

Top
#49369 - 03/05/05 04:00 AM Re: bonding electrodes, separate buildings(common area circuits
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
210.25 prohibits branch circuits from one dwelling to supply common area lighting.

IMO...you will need a third meter for common area lighting.

I would just wire the lighting for the each side of the buildings area from that sides service.

shortcircuit

Top
#49370 - 03/05/05 08:07 AM Re: bonding electrodes, separate buildings(common area circuits
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
the services are located on each builing,about 200 feet apart, this is a multifamily structure with a firewal. My concerns were because both building security lights are supplied from one owner's panel, the electrodes from both buildings should be bonded ?

Top
#49371 - 03/07/05 01:54 PM Re: bonding electrodes, separate buildings(common area circuits
boggerbutt2454 Offline
Member

Registered: 02/27/05
Posts: 44
Loc: Concord NC USA
If this is a multi-family building why didn't you provide for a house panel? I hope the owner of the panel feeding the security lights never gets mad at his neighbors!!

Top
#49372 - 03/07/05 04:37 PM Re: bonding electrodes, separate buildings(common area circuits
hbiss Offline
Member

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
210.25 prohibits branch circuits from one dwelling to supply common area lighting.

Yup, I missed that one. Shows how much multifamily I do.

I assumed that the owner would occupy the unit with the lights on his meter. Even if this were allowed what happens if the unit gets sold?

I agree with the others- either split the lighting up and put it on the respective meters or provide a house meter. I think which way to go would depend on the layout and where the lighting is located. I don't think any unit should be paying for site lighting.

-Hal
_________________________
www.myphonetechs.com

Top
#49373 - 03/07/05 05:17 PM Re: bonding electrodes, separate buildings(common area circuits
Gregtaylor Offline
Member

Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
A little off the actual question, I guess, but I'm confused about the actual building. Is this one(1) building or two(2)? If they are physically attached in any way above ground they are a single building. Why are there 2 services? Or am I reading this wrong?

Sorry, brain fade I guess. I see the situation now. But still, you can't feed house lighting from one service if it penetrates the other living space. That's what the firewall is there for to begin with.

[This message has been edited by Gregtaylor (edited 03-07-2005).]