The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#4930 - 10/23/01 05:25 PM Polarization help
dzmacdvm Offline
Junior Member

Registered: 10/23/01
Posts: 4
I recently installed a new circuit. The wiring runs to a 2 gang box with 2 switches where the hot wire is shared via pigtail. One of the switches runs to 3 consecutive fixtures (recessed lights) and the run ends in a receptacle (outlet). When I connect the black wire to the brass screws and the white lead to the silver screws and the ground to the ground screw and test this outlet, the polarization detector indicates that the hot and neutral wires are opposite. The light indicator shows correct polarization when/if I connect the black lead to the silver side and vice versa which I know should be wrong. Is the problem at the level of the switch where the hotwire is shared? Or how else could these 2 be opposite? Any suggestions greatly appreciated. Thank you.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#4931 - 10/23/01 06:43 PM Re: Polarization help
spkjpr Offline
Member

Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
What does the second switch control? I also seem to remember an articlle about neon tpolarity testers being fooled if the circuit has any other neutral connections. Will try to find the article, believe it came from ECM Magazine.

Top
#4932 - 10/23/01 07:32 PM Re: Polarization help
dzmacdvm Offline
Junior Member

Registered: 10/23/01
Posts: 4
The second switch also controls recessed lights but on a dimmer. Put on 2 switches because didn't want all on dimmer and dimmer switch cant handle the load of all of them. So youre saying that though I have it wired correctly, the detector might not be accurate in this instance? The tester I'm using is a 3 prong with 3 light indicator, not very sophisticated.

Top
#4933 - 10/23/01 07:37 PM Re: Polarization help
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Where did you pick up power for this new circuit?

Top
#4934 - 10/23/01 08:39 PM Re: Polarization help
dzmacdvm Offline
Junior Member

Registered: 10/23/01
Posts: 4
Added a 15Amp breaker at panel specifically for this lighting project.

Top
#4935 - 10/23/01 08:57 PM Re: Polarization help
amp-man Offline
Member

Registered: 06/23/01
Posts: 144
Loc: Sacto, California US of A
DZ,

I suspect that you've flipped the hot & neutral at one of the light fixtures.

In telco parlance, a "crossed pair".

Remove the lamps in the three fixtures and get yourself a good grounding conductor reference (like the ground pin of an extention cord plugged into an outlet that tests out good; or the metal housing of the can light, if that's what you're dealing with). With the circuit off, starting at the fixture first in line from the switch, check continuity between known ground and the lampholder shell. The fixture where you lose continuity is the mis-wired one. The shell should be connected to the grounded conductor...with H and N flipped, the shell would be hot & the button neutral. The dumb lamp doesn't know any better, it'll still work...

You could test the circuit hot using a test light or voltmeter, but it's safer testing it cold, using a continuity buzzer.

Work safe,

Cliff

Top
#4936 - 10/23/01 09:58 PM Re: Polarization help
dzmacdvm Offline
Junior Member

Registered: 10/23/01
Posts: 4
Thanks Cliff, will give it a test. I appreciate your time.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals