The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Topic Options
Rate This Topic
#49159 - 02/28/05 01:40 PM Service Entrance GFP Testing per (NFPA70-B)
jkochan Offline
Member
Registered: 01/19/05
Posts: 61
Loc: Phoenix, AZ USA
We have received a notice that GFP testing on our SES is due (from the Co. that installed it). While we are pro-active in our preventative maintenance on this building, the Property manager is concerned about cost and down time. Since our insurance carrier has not required this test yet, is it necessary? Is this testing best done by the power company or a private contactor? Since the very thought of a deliberate power-down of the building has everyone wringing their hands in anguish, can someone give me an idea of the time frame for this test?
Top
Work Gear for Electricians and the Trades
#49160 - 03/01/05 09:03 PM Re: Service Entrance GFP Testing per (NFPA70-B)
dmattox Offline
Member
Registered: 10/20/04
Posts: 267
Loc: Anaheim, CA
There are private companies that will test it, I think it costs us around $500 here in SoCal. Downtime is minimal, like 1/2 hour max. The only times we have had people do it are when inspectors require it for a new building, or if a plant is having problems with it tripping. I can't recall a facility that checks it as a preventative maintenance requirement, not to say that it shouldn't be tested.
Top
#49161 - 03/02/05 10:13 AM Re: Service Entrance GFP Testing per (NFPA70-B)
jkochan Offline
Member
Registered: 01/19/05
Posts: 61
Loc: Phoenix, AZ USA
Thanks for your reply. We duly notified the next rung up on the food chain of the reason for the test and the NFPA recommendation to do so. Since no one will take the time to look up NFPA 70-B, it will most likely languish in his or her in-box for eternity or until the insurance carrier takes notice.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 105 Guests and 18 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals