#49044 - 02/25/05 03:41 PM arc fault circuit breakers and knob and tube
jdp Offline
Junior Member
Registered: 12/21/04
Posts: 1
Loc: blackstone massachusett
Are arc fault cicuit breakers required in Massachusett on service upgrades? I heard of other electrical contractors having trouble when mandated to use arc fault circuit breakers on knob and tube. Any one else out there having these problems, please advise thank you JDP
Top
Work Gear for Electricians and the Trades
#49045 - 02/25/05 04:48 PM Re: arc fault circuit breakers and knob and tube
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Massachusetts did put a revision in the 2002 MEC 210.12(C) that read:

(C)Overcurrent Device Replacements.
Where panelboards are replaced that contain one or more circuits requiring AFCI protection by this or other sections of the Code, AFCI protection shall be provided for such circuits.

This revision was quickly removed and did not make it into the 2005 MEC. Although it may be around for the 2008 cycle if manufacturers can produce products that satisfy the AFCI requirements under all circuiting arrangements.

shortcircuit
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals