The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#49044 - 02/25/05 03:41 PM arc fault circuit breakers and knob and tube
jdp Offline
Junior Member

Registered: 12/21/04
Posts: 1
Loc: blackstone massachusett
Are arc fault cicuit breakers required in Massachusett on service upgrades? I heard of other electrical contractors having trouble when mandated to use arc fault circuit breakers on knob and tube. Any one else out there having these problems, please advise thank you JDP

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#49045 - 02/25/05 04:48 PM Re: arc fault circuit breakers and knob and tube
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Massachusetts did put a revision in the 2002 MEC 210.12(C) that read:

(C)Overcurrent Device Replacements.
Where panelboards are replaced that contain one or more circuits requiring AFCI protection by this or other sections of the Code, AFCI protection shall be provided for such circuits.

This revision was quickly removed and did not make it into the 2005 MEC. Although it may be around for the 2008 cycle if manufacturers can produce products that satisfy the AFCI requirements under all circuiting arrangements.