#49031 - 02/24/05 08:55 PM Wiring Methods
sierra electrician Offline
Member
Registered: 02/12/05
Posts: 220
Loc: North Fork, CA USA
I new to this board and you might of already coverd this.
On the photo section of this board there is a thread that asks members to send pics of of what you look like. One gentleman has his pic standing in front of a laod center which has surface (exposed) mounted romex neatly stapled to the backboard entering the side of the load center, each one in its own connector. Is that leagal where he is from? Does he live in another country?
I'm just curious.
Rob
Top
Work Gear for Electricians and the Trades
#49032 - 02/24/05 09:42 PM Re: Wiring Methods
stamcon Offline
Member
Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
I believe you referring to Ed MacLaren and he is from Canada. I would have to say yes it's legal to run the NM like that. This might be debatable, but I feel that 336-6(a) of the 99NEC allows it, as it closely follows the surface of the structure. Some might argue that it's still subject to physical damage.

steve
Top
#49033 - 02/24/05 11:10 PM Re: Wiring Methods
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
How else would you bring RX out of a panel in a residence?
I suppose if you are in one of the "pipeland" areas the whole Romex thing is foreign but stapling it up a running board is the usual way if it is not exposed to physical damage.
_________________________
Greg Fretwell
Top
#49034 - 02/25/05 09:38 AM Re: Wiring Methods
sierra electrician Offline
Member
Registered: 02/12/05
Posts: 220
Loc: North Fork, CA USA
gfretwell
Here you would have to build a chase and enclose the NM.
Rob
Top
#49035 - 02/25/05 11:21 AM Re: Wiring Methods
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Protecting Romex does seem to be a local option thing. I have lived in places that think, stapled to a running board in unfinished areas, is fine. Other places want varying degrees of protection.
_________________________
Greg Fretwell
Top
#49036 - 02/25/05 03:23 PM Re: Wiring Methods
pauluk Offline
Member
Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Here you go:

Top
#49037 - 02/25/05 04:21 PM Re: Wiring Methods
derater Offline
Member
Registered: 03/30/02
Posts: 182
In the photo, I'm curious about the panel brand; is the lug area cover desirable or not?OK, 2nd look and I think it's a Sq.D
About that cover though.....
Top
#49038 - 02/25/05 04:24 PM Re: Wiring Methods
CRM Offline
Member
Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
I'm also from Canada and I will tell you Ed's installation is 100% legal. The code allows loomex to be run on the surface if it is 5 feet or higher and not subject to mechanical damage. The cable is not subject to mechanical damage stapled to a backboard then run into a panel, how would this cable ever be damaged? To answer your question Derater, the Canadian Electrical Code requires a steel barrier to separate the service conductors from the branch circuit area, the panel is a square D.

[This message has been edited by CRM (edited 02-25-2005).]
Top
#49039 - 02/25/05 05:15 PM Re: Wiring Methods
OreElect Offline
Member
Registered: 03/05/04
Posts: 96
Loc: Salem,Oregon.USA
334.15(B)( Amendment ) Exposed nonmetallic sheathed cable shall be protected where it is installed horizontally below 8 feet above the floor.Exposed nonmetallic sheathed cable below 8 feet above the floor that enters the top or bottom of a panelboard shall be protected from physical damage by conduit,1/2 plywood or 1/2 drywall.
Top
#49040 - 02/25/05 05:28 PM Re: Wiring Methods
CTwireman Offline
Member
Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
I don't see what the big deal is. It's funny how some areas of the country have so much Romex Phobia.

Ed's picture shows a widespread, standard practice (minus the separate compartment for the service conductors of course. ) in my area.

Peter
_________________________
Peter
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
48 minutes 0 seconds ago
Looking for older post
by sparkyinak
Today at 12:27 AM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 92 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 03/13/07
Posts: 167

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals