The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#48386 - 02/10/05 09:05 AM New 3" hub code for Resi Load Centers??
BillK Offline
Junior Member

Registered: 12/22/04
Posts: 3
Loc: South Elgin,IL ,USA
Has anybody heard anything about new codes reguarding 3" hubs to a residential load center? Anybody have details???
Have heard it might be for panels 400A and up.
_________________________
Bill K

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#48387 - 02/10/05 04:14 PM Re: New 3" hub code for Resi Load Centers??
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
Hi Bill,

I have not heard anything.
310.15(B)(6) allows 400 KCMIL THWN copper for a 400 amp dwelling service.
You could go traditional and use 500 KCMIL THWN, both fit in 2 1/2 per Annex C - Table C1 EMT and C4 IMC. In table C8 for RMC, 500 KCMIL would have to be in 3 inch.

Top
#48388 - 02/10/05 07:00 PM Re: New 3" hub code for Resi Load Centers??
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Bill:
Welcome to the forums.....
Could you be refering to a utility (POCO) requirement???

Here in NJ (PSE&G) a 'mast' service requires a 2 1/2" RGC minimum.

John
_________________________
John

Top