Has anybody heard anything about new codes reguarding 3" hubs to a residential load center? Anybody have details???
Have heard it might be for panels 400A and up.
_________________________
Bill K
Top
Work Gear for Electricians and the Trades
#48387 - 02/10/05 04:14 PM Re: New 3" hub code for Resi Load Centers??
russ m Offline
Member
Registered: 02/22/03
Posts: 169
Loc: Burbank,IL,USA
Hi Bill,

I have not heard anything.
310.15(B)(6) allows 400 KCMIL THWN copper for a 400 amp dwelling service.
You could go traditional and use 500 KCMIL THWN, both fit in 2 1/2 per Annex C - Table C1 EMT and C4 IMC. In table C8 for RMC, 500 KCMIL would have to be in 3 inch.
Top
#48388 - 02/10/05 07:00 PM Re: New 3" hub code for Resi Load Centers??
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Bill:
Welcome to the forums.....
Could you be refering to a utility (POCO) requirement???

Here in NJ (PSE&G) a 'mast' service requires a 2 1/2" RGC minimum.

John
_________________________
John
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (Admin), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals