The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Ruben Rocha), 96 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#48314 - 02/09/05 07:18 AM Confused about transformers
swampy Offline
Junior Member

Registered: 02/09/05
Posts: 1
Loc: Bancroft, WI U.S.
I 'm studying for my Journeyman's. One question is ; A 10 kva trans. is 240/120v. step down. secondary ocp is 125%. What is max. cb required for primary if eff. is 100%?

Can anyone give me some pointers? Thank you!

Top
Work Gear for Electricians and the Trades
#48315 - 02/09/05 08:20 AM Re: Confused about transformers
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
The formula for pri current is kVA/E pri times the phase multiplier. In this case a single-phase multiplier is 1. If it were 3 phase the multiplier would be 1.73.

It would be a good idea to read section 450.3(B) and study the table. You should understand that in general a transformer operating at 600V or less is considered (in general) when the pri OCPD is set at 125% of the pri FLC) The table will go on to indicate that in cases where there is OCP at the secondary of the transformer which is set at 125% of the secondary FLC, the pri OCPD may be increased to 250% of pri FLC.

Your transformer should have a 41A pri and 2.5 X 41 yield 102. (see notes to tables ) I'd call it 100A.

Top
#48316 - 02/09/05 08:33 PM Re: Confused about transformers
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Cpal said "Your transformer should have a 41A pri and 2.5 X 41 yield 102. (see notes to tables ) I'd call it 100A."
That is correct. Note that the table allows you to go up to 250% but not exceed that figure. If the 250% does not yeild a standard
fuse or breaker, you may not round up.