#48268 - 02/07/05 12:59 PM Overhead 400A service
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
What do you guys use for the service drop wires? In PVc

500mcm copper thhn?
600 alum?
And the same question for wiring into the panels, in pvc,
2/0 copper, 3/0 alum
just curious of the costs.
Top
Work Gear for Electricians and the Trades
#48269 - 02/07/05 01:02 PM Re: Overhead 400A service
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
parallel 250 kcmil alum.
_________________________
Earl
Top
#48270 - 02/07/05 02:48 PM Re: Overhead 400A service
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
parallel 250 kcmil alum


Boy if those are in the same raceway that is pushing it as much as possible and is only acceptable if the calculated load is less than 368 amps.

250 AL rated 230 amps @ 90 C, four current carrying conductors in a raceway.

230 x 2 x .8 = 368 amps.

240.4(B) allows the next standard breaker however the calculated load must stay below 368 amps.

The last 400 amp overhead I did used one set of 600 Kcmil copper.

In my opinion you are not providing a 400 amp service with 500 kcmil copper (380 amps) or two sets of 250 kcmil aluminum (368 amps).

The service can only be rated as high as the lowest rated component.

Of course take this all for what it's worth, I do commercial work so Table 310.15(B)(6) is out of the question.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#48271 - 02/11/05 11:13 AM Re: Overhead 400A service
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Just bringing this up to the top, I was hoping for some more comments.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#48272 - 02/11/05 11:35 AM Re: Overhead 400A service
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Bob:
OK, it's on top, I'll bite...
500kcmil cu; 4" PVC or RGC dependent on spec's. Occasionally 600 al, but that's a rare bird.

UG is PVC, unless the 1 PE does the spec....
last time I got a change order & spec change in "clouds" when I verified the $$$ of RGC.

Going to the panels....cu, usually 4/0.

John
_________________________
John
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals