#48215 - 02/06/05 09:52 AM Floor Heat
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
We have a bathroom with the tile floor heating comming up. We done them before but was wondering somthing. If the tile guys leave way to much heating wire in your box can it be cut to fit? Or does that case problems with the resistancee? Can it be put in the box or will the box get too hot. Do we just need to make sure the tilers use up the extra wire in the floor and not the box?

If I remember on 1 mat there are 2 leads with a metal sheald. The shield would be grounded?

Tom
Top
Work Gear for Electricians and the Trades
#48216 - 02/06/05 10:07 AM Re: Floor Heat
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
The heating leads should never leave the floor. The non-heating leads can be cut as desired and yes the shield should be connected to the EGC.

Curt
_________________________
Curt Swartz
Top
#48217 - 02/06/05 01:39 PM Re: Floor Heat
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
OK. So the leads going to the controler don't heat up.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals