The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (sparkyinak, LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#48157 - 02/04/05 09:52 PM Isolated Ground
buck Offline
Member

Registered: 02/01/05
Posts: 19
Loc: Everett, WA USA
I have a requirement to provide an isolated ground. The customer has asked for the Isolated ground wire to originate at the secondary side of the transformer, XO, and be brought into the panel and landed on an isolated ground bar. I have an existing 1200 amp 120/208 three phase service, exterior meter pack system. The utility transformer is about thirty feet away and comes right into two 600 amp disconnects. The service is grounded/bonded to the water and ground rods per NEC. From this point on the neutral is floating to individual retail locations. I have pulled into the same conduit an isolated ground wire and landed it on an isolated ground bar. Even though it may be isolated it is still electrically the same wire because it is terminated at the same point as the equipment ground.
Is this not a permissible installation of an isolated ground?

The equipment being served is a 30kVA UPS and Telephone Switching gear.
_________________________
Buck

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#48158 - 02/05/05 06:02 AM Re: Isolated Ground
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I don't believe that your utility company is going to provide you with an isolated ground back to Xo on their transformer.

As far as I can tell, you have met the NEC code requirements. I'm glad they didn't ask you to run this isolated ground to an individual ground rod as so many end users do.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#48159 - 02/05/05 06:08 AM Re: Isolated Ground
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
It should not run back to XO in this case.

In this case running it to the location of the Main bonding jumper at the service disconnect is the correct way to do it.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#48160 - 02/05/05 07:46 AM Re: Isolated Ground
dereckbc Offline
Member

Registered: 10/08/03
Posts: 158
Loc: Tulsa, OK
Buck, I think your customer has recieved some information from an engineer or technician who is stating IEEE Emerald specifications, and has confused him/herself.

Emerald specs do call for the IG to originate on the Xo of a customer owned isolation transformer, not a utility owned transformer. As stated already what your customer is asking for will not be permitted by the utility. It would be nice if the utility would supply EGC circuits, but it is not going to happen.

For your application the IG has to originate from the in the disconnect that contains the N-G bond point.

If your customer wants a IEEE spec IG ground, they would need to install a shielded isolation transformer to supply the Telco equipment. This is a common practice, but it is not supplied by the utility. Hope this helps...

Top
#48161 - 02/05/05 12:32 PM Re: Isolated Ground
buck Offline
Member

Registered: 02/01/05
Posts: 19
Loc: Everett, WA USA
Thank you all for your replies. I'll have to try and educate my end user who took a two day seminar on grounding. Again, thank you.
Rick Buck
_________________________
Buck

Top
#48162 - 02/05/05 02:15 PM Re: Isolated Ground
dereckbc Offline
Member

Registered: 10/08/03
Posts: 158
Loc: Tulsa, OK
Buck, now it makes sense. Your client took a ground class and heard the IG should originate from the Xo which is 100% true, except in this case.

Top
#48163 - 02/05/05 08:22 PM Re: Isolated Ground
dereckbc Offline
Member

Registered: 10/08/03
Posts: 158
Loc: Tulsa, OK
Buck, FWIW I assume your client is going to use the IG circuit to feed a UPS, and the UPS is supplying the telephone equipment. If that is the case an IG is not nessecary to feed a UPS.

Top
#48164 - 02/05/05 08:25 PM Re: Isolated Ground
buck Offline
Member

Registered: 02/01/05
Posts: 19
Loc: Everett, WA USA
yes, you are absolutely right. Thanks for the second opinion. Buck
_________________________
Buck

Top
#48165 - 02/07/05 09:19 PM Re: Isolated Ground
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Bob is right. An IG for computer stuff should land on the same bus as the main bonding jumper and ground electrode conductor. You want a "star" originating at the MBJ/GEC junction. Grounding should then branch from there in a tree structure so there is no parallel path.
Back in the day we never brought a neutral to a computer room panel (all L/L loads) and we used the isolated neutral bus for the IG. Equipment and raceway grounding was on the bonded supplimental bus.
(In a prior life I was an IPR for IBM designing computer rooms).
_________________________
Greg Fretwell

Top
#48166 - 02/07/05 10:00 PM Re: Isolated Ground
buck Offline
Member

Registered: 02/01/05
Posts: 19
Loc: Everett, WA USA
Thank you for the info. - Buck
_________________________
Buck