The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Looking for older post
by Admin
01/20/17 11:05 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
Safety at heights?
by Trumpy
01/20/17 09:13 PM
Webmaster > Admin
by Trumpy
01/20/17 08:29 PM
Live Chat Feature
by Admin
01/20/17 07:36 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 17
Ruben Rocha 17
gfretwell 15
Who's Online
2 registered (Admin, Trumpy), 162 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#48075 - 02/03/05 05:47 AM EGC sizeing
JCooper Offline
Member

Registered: 12/30/02
Posts: 229
Loc: Kendall Park, NJ USA
Hello all, I have an existing Infared electric heater installed, nameplate amps is 25, OCP 30 amps, fed with #8 THWN in 3/4" flex. I am adding another heater right next to this one and I just wanted to make sure that I can share the #8 EGC I pulled the first time, I will just be adding the two ungrounded conductors to feed the second unit in the same raceway. I looked in 250.122 and for 30 ocp the min EGC is #10, and for 60 amp, which would be the total amps drawn by both units the EGC is still #10 so my #8 should be fine, right? Thanks

Jim

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#48076 - 02/03/05 05:54 AM Re: EGC sizeing
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
The EGC should be sized dependant upon the breaker that it needs to trip. For the 30 amp, #10 is typically fine, however, you increased the size of the ungrounded conductors (for voltage drop?), and therefore the EGC must be increased in proportion, requiring a #8 EGC. It sounds to me like your EGC size will be fine.
_________________________
Ryan Jackson,
Salt Lake City

Top
#48077 - 02/03/05 06:25 PM Re: EGC sizeing
JCooper Offline
Member

Registered: 12/30/02
Posts: 229
Loc: Kendall Park, NJ USA
Sorry, I forgot to include that, the run is about 100' so I ran the #8 for VD. I thought the egc was alright, I just wanted to make sure I didn't miss something. Thanks

Jim