The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#48006 - 02/01/05 05:19 PM Connecting two ground rods
eswets Offline

Registered: 03/07/04
Posts: 56
Loc: Lansing, IL, USA
I did a service the other day, and the inspector wants me to install a second ground rod 6' away even though it is less than 25ohms. Im not going to argue, b/c I will get paid to do it, but I need to know how to connect the other ground rod. Most other EC I'ved talked to never had to do this. Can I just run direct burial wire in the ground from the 1st G.R. to the second or each from the ground lug?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#48007 - 02/01/05 05:30 PM Re: Connecting two ground rods
NJwirenut Offline

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
You must have real good soil conductivity to get below 25 ohms with one rod.

I generally just run a continuous GEC from the panel, to one rod, then to the next rod.Leave the wire on the surface, and bury it in a shallow trench after inspection....

#48008 - 02/01/05 05:31 PM Re: Connecting two ground rods
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I've done this several times. I connect rod #2 to rod #1 with one length of wire & connectors (all of ours should be exposed, in pipe here). Another wire connects rod #1 to the panel.

#48009 - 02/01/05 06:27 PM Re: Connecting two ground rods
richard Offline

Registered: 08/07/03
Posts: 84
Loc: L.I. New York
you should check with the poco or inspector in your area. We had to have one wire from each rod to the meter base.

#48010 - 02/01/05 06:44 PM Re: Connecting two ground rods
Electricmanscott Offline

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
If your under the NEC and it is less than 25 ohms why are you still going to do it? Anyway just dig a small trench between the rods and run the wire between them. Connect to each rod and you are done. Until the inspector comes up with something else he would like you to do.

#48011 - 02/02/05 05:07 AM Re: Connecting two ground rods
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
How did you test it to find that it is less than 25 ohms?

#48012 - 02/02/05 12:53 PM Re: Connecting two ground rods
Belgariad Offline
New Member

Registered: 05/17/02
Posts: 9
Loc: Linwood, NC, United States
All inspectors in my area that I've dealt with require two ground rods. Also I have failed for not having a continuous wire from meter base to both rods.

#48013 - 02/02/05 12:54 PM Re: Connecting two ground rods
Trumpy Offline


Registered: 07/05/02
Posts: 8532
Loc: SI,New Zealand
How did you test it to find that it is less than 25 ohms?

Good point.
There are ready made clamps for this very thing.
Personally I'd just use a single heavy wire between the two rods.
Let's face it, these days if you're not young, you're old - Red Green grin

#48014 - 02/02/05 02:46 PM Re: Connecting two ground rods
detubbs Offline

Registered: 11/18/04
Posts: 52
Loc: PA
we do one continuous run of bare copper #6 here in our area. one end in the panel one rod just outside the building and one a ground rod length away. this is pretty much standard in our area. our inspectors and poco's want it this way if possible, plus it's easy and fewer house penetrations to do it this way when your installing or replacing a service.

#48015 - 02/02/05 03:47 PM Re: Connecting two ground rods
luckyshadow Offline

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
The county I live in in Maryland has been requiring 2 rods for last couple years now.
When I wired my house I ran one # 6 out of the panel through the clamp on rod # 1 then over to rod # 2. One wire two rods . Now I hear the county wants footer gronds instead of rods.