#47761 - 01/26/05 04:55 AM Oversized Buck-boost?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I am working with a 7 1/2 HP Air Compressor motor.
It is 240V 28A 1Ph.
The system voltage is 208.
Someone installed a 3kVA Buck-Boost, but the website for Jefferson Electric (transformer manufacturer)lists a 1kVA unit (minimum) for a 7 1/2 HP motor.
I don't see a problem with an oversized unit, but am not sure.
Anyone have any insight?

Thanks.
Top
Work Gear for Electricians and the Trades
#47762 - 01/26/05 05:59 AM Re: Oversized Buck-boost?
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
I see no significant safety or functionality issues with a larger buck-boost. It might even provide better motor starting.

The larger core will mean more core losses over the life of the unit, even when the air compressor is off.

-Jon
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals