#4767 - 10/15/01 10:34 AM EXIT signs  
donles  Offline
Member
Joined: Apr 2001
Posts: 83
Pennsylvania
I was called to a small office building to relamp their exit signs and they asked about adding some signs in another part of the building. One thing I noticed with the existing signs is that they are dark upon loss of power. They have no backup battery and the building does not have an emergency power generator. So I was wondering what the proper application of EXIT signs is?
Does the situation call for battery-backed EXIT signs?
Don


Work Gear for Electricians and the Trades

#4768 - 10/15/01 12:36 PM Re: EXIT signs  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
This is a pretty tricky area. The NEC does not require exit signs. They are required by OSHA, the Life Safety Code and building codes for most occupancy. If your building did not legally require an emergency system, and it seems it didn’t, only a reliable source of power is required. That is not necessarily generator or battery backed. The installation is probably OK. If the building were legally required to have an emergency system the exit signs would have to be wired per NEC article 700. This would require a second source of power.
Nick


#4769 - 10/15/01 12:52 PM Re: EXIT signs  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Here in Minneapolis, the Fire Marshall determines the location, type and retrofit requirements. The Electrical Inspector sees that the power is installed to the NEC.

Al


Al Hildenbrand


Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.7491 MB (Peak: 0.8737 MB) Zlib enabled. Server Time: 2017-03-29 03:24:00 UTC