The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#47440 - 01/17/05 04:31 AM Buck Booster
Dave55 Offline
Member
Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I'm installing a 0.5 KVA transformer for a tanning bed. The house voltage is 251V 1PH and I need to bring it down in the 215-230 range. The manufacturer of the tanning bed is shipping the transformer with the bed. I haven't installed one this small before, and am curious about it's size.

Is this going to require a separate cabinet, or will it fit in the distribution panel? Will it require some type of ventilation?

Dave
Top
Work Gear for Electricians and the Trades
#47441 - 01/17/05 04:40 AM Re: Buck Booster
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Dave any buck boosts I have installed have looked like this



This one happens to be .5 KVA so the size will be approximately the same as yours.

6" x 6" x 5" don't count on those measurements but it will be somewhat close.

I usually put these right at the panel.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#47442 - 01/17/05 06:43 AM Re: Buck Booster
circuit man Offline
Member
Registered: 11/05/01
Posts: 287
Loc: saluda,s.c.
dave, why is the house voltage so hi?it should be around 240 or a couple above.i bet electronics don't last long.have they contacted the power company about this?
Top
#47443 - 01/17/05 06:44 AM Re: Buck Booster
circuit man Offline
Member
Registered: 11/05/01
Posts: 287
Loc: saluda,s.c.
is this a single phase service? not from a three phase bank.

[This message has been edited by circuit man (edited 01-17-2005).]
Top
#47444 - 01/17/05 06:51 AM Re: Buck Booster
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Circuitman 251 volts is a little under 5% high, it is not that bad.

You could talk to the power company I doubt they would do anything.

UL requires equipment to handle + or - 10%
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#47445 - 01/17/05 07:22 AM Re: Buck Booster
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
To go on a little I will show some info from "Voltage Ratings for Electrical Power Systems and Equipment, American National Standard ANSI C84.1–1989"

The power company does not have to follow this but they may.

For a 120/240 3 wire service the voltage at the service should be between 91.7% (220 volts) and 105.8% (254 volts)

The voltage at the utilization equipment should be between 88% (212 volts) and 105.8% (254 volts)

You can get more info with an Internet search for ANSI C84.1–1989

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#47446 - 01/17/05 07:27 AM Re: Buck Booster
Dave55 Offline
Member
Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I don't know much about POCO stuff, but I'd say it's intentionally set at the high end so a voltage drop will keep it in range.

Dave
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals