The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
0 registered (), 0 Guests and 211 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#47417 - 01/16/05 01:36 PM 400 amp service
eswets Offline
Member

Registered: 03/07/04
Posts: 56
Loc: Lansing, IL, USA
The state I used to work it, it was common pratice for a 400amp residential service to really be a 320amp. The meter was a 320amp rated meter socket that feed 2 200amp (main breaker) panels with 2" pipes and 3/0's to each panel. I have changed to a different region, and am wondering if this is standared everywhere or if this is not the right way to do this.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#47418 - 01/16/05 01:43 PM Re: 400 amp service
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
It is fine, a 320 meter is rated 320 amps continuous, 400 amps non-continuous.

If a 400 amp service is properly sized it will not exceed 320 amps continuously.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#47419 - 01/16/05 03:23 PM Re: 400 amp service
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
Common practice in Mass. 320 amp continuous for a 400 amp service. 80%. I believe you have to be the full 400 amp on commercial services. Most of the electricians around here install it exactly how you explained except they use 4/0-3 SEU/AL. No pipe. Your way is much better, I guess around where I am they go the bare minimum requirements.

Top
#47420 - 01/16/05 04:43 PM Re: 400 amp service
ToHo Offline
Member

Registered: 12/29/04
Posts: 46
Loc: N.Y.
wirenutt.. what do you guys in Mass. run for 400amp UG services?? what would be a typical meter and panel configuration be. Thanks..ToHo

Top
#47421 - 01/16/05 04:55 PM Re: 400 amp service
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Quote:
I believe you have to be the full 400 amp on commercial services.


The only reason I can see that requirement is if you used 100% rated breakers and equipment.

A typical 400 amp breaker is only UL listed for 320 amps continuous or 400 amp non-continuous.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#47422 - 01/16/05 05:28 PM Re: 400 amp service
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
Thats how the 400 amp resedential are set up around here in IL. We don't call it a (2) 200 or 320 amp. Maybe more of a sales thing. Don't want to be pricing out a 320 amp when the other EC has the same set up calls it a 400 amp.

Tom

Top
#47423 - 01/16/05 06:12 PM Re: 400 amp service
eswets Offline
Member

Registered: 03/07/04
Posts: 56
Loc: Lansing, IL, USA
Tom,
Im in IL I think around your area. Suburbs of Chicago. So using a 320amp meter socket with 2/200amp panels is ok for the 400 amp service?

Top
#47424 - 01/17/05 03:11 PM Re: 400 amp service
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
Yep.

At the supply we just ask for a 400 amp pedistal but they know we mean 320 amp. Milbanks catolog for Com Ed only shows single phase 320 not 400 amp meter housings. Com Ed resi feeds underground are normaly 200 and 320 a. Overhead 100, 200, and 320 a.

We would only bond one panel and would run a larger water pipe ground than a single 200 a service, I think 1ott. You could do it other ways.

Tom

Top
#47425 - 01/17/05 04:28 PM Re: 400 amp service
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
TOHO; Mostly the Milbank # 2448-X meter socket. One EC uses 500 kcmil xhhw. Murray also makes a unique 400 amp double main break panel that's kind of interesting. Guess it depends on your situation.

Top
#47426 - 01/17/05 08:37 PM Re: 400 amp service
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Tom
What do you mean by, "bond only one panel"?

Pierre
_________________________
Pierre Belarge

Top