#46957 - 01/06/05 02:37 PM Isolated Ground receptacle with 2 grounding screws
SparkyOhio Offline
Junior Member
Registered: 01/06/05
Posts: 1
I was wondering if anyone has ever seen a isolated ground receptacle with two grounding screws. I know that they have a grounding screw for the isolated ground conductor, but i was wondering if they make one that has a grounding screw for the other grounding conductor.
Top
Work Gear for Electricians and the Trades
#46958 - 01/06/05 03:13 PM Re: Isolated Ground receptacle with 2 grounding screws
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
I have never seen such, and believe that such would be essentially useless.

An isolated ground receptacle is only potentially of use in an environment where there is current flow or electrical noise on the grounding system. For example, even in a _properly_ installed metal raceway system, you almost certainly will have loop paths described through the grounded metal. You will almost certainly have changing magnetic flux coupled through these loops, and thus current flow on the ground system.

I suppose you could also have electrostatic pickup by the ground conductor; a isolated ground conductor surrounded by a metal raceway would be shielded from this.

But in any of these metallic systems, the yoke of the isolated ground receptacle will be properly grounded through the metal receptacle box. No need for a second screw.

Now consider an isolated ground receptacle in a non-metallic box. Clearly the yoke is not properly grounded...but on the other side of the coin, a $0.39 Home Depot special in a non-metallic box essentially has an isolated ground. Use a non-metallic wiring method, and a single receptacle on the circuit, and if the run is back to the main panel, then you have something that is electrically an 'isolated ground' receptacle.

-Jon
Top
#46959 - 01/06/05 03:26 PM Re: Isolated Ground receptacle with 2 grounding screws
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Perhaps it is to bond a metal faceplate?
_________________________
Ryan Jackson,
Salt Lake City
Top
#46960 - 01/06/05 04:43 PM Re: Isolated Ground receptacle with 2 grounding screws
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
No, what for? Mount the receptacle in a metal box and you don't need it. Use a plastic box and you don't need a separate isolated ground or an IG receptacle.

-Hal

[This message has been edited by hbiss (edited 01-06-2005).]
_________________________
www.myphonetechs.com
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals