The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 281 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#46957 - 01/06/05 02:37 PM Isolated Ground receptacle with 2 grounding screws
SparkyOhio Offline
Junior Member

Registered: 01/06/05
Posts: 1
I was wondering if anyone has ever seen a isolated ground receptacle with two grounding screws. I know that they have a grounding screw for the isolated ground conductor, but i was wondering if they make one that has a grounding screw for the other grounding conductor.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#46958 - 01/06/05 03:13 PM Re: Isolated Ground receptacle with 2 grounding screws
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I have never seen such, and believe that such would be essentially useless.

An isolated ground receptacle is only potentially of use in an environment where there is current flow or electrical noise on the grounding system. For example, even in a _properly_ installed metal raceway system, you almost certainly will have loop paths described through the grounded metal. You will almost certainly have changing magnetic flux coupled through these loops, and thus current flow on the ground system.

I suppose you could also have electrostatic pickup by the ground conductor; a isolated ground conductor surrounded by a metal raceway would be shielded from this.

But in any of these metallic systems, the yoke of the isolated ground receptacle will be properly grounded through the metal receptacle box. No need for a second screw.

Now consider an isolated ground receptacle in a non-metallic box. Clearly the yoke is not properly grounded...but on the other side of the coin, a $0.39 Home Depot special in a non-metallic box essentially has an isolated ground. Use a non-metallic wiring method, and a single receptacle on the circuit, and if the run is back to the main panel, then you have something that is electrically an 'isolated ground' receptacle.


#46959 - 01/06/05 03:26 PM Re: Isolated Ground receptacle with 2 grounding screws
Ryan_J Offline

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Perhaps it is to bond a metal faceplate?
Ryan Jackson,
Salt Lake City

#46960 - 01/06/05 04:43 PM Re: Isolated Ground receptacle with 2 grounding screws
hbiss Offline

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
No, what for? Mount the receptacle in a metal box and you don't need it. Use a plastic box and you don't need a separate isolated ground or an IG receptacle.


[This message has been edited by hbiss (edited 01-06-2005).]