#46869 - 01/04/05 06:01 PM Building Disconnect
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Today at the supply house I asked for a Nema 3R 240 volt 60 amp single phase non-fusible disconnect switch suitible for service equipment.Well they came out with a 3-pole safety switch.

I want to use this for a Building Disconnecting Means on the exterior of the accessory building before entering to the panel.My overcurrent protection is where the feeder originates.

Maybe it is more common to use a Nema 3R circuit breaker enclosure with a circuit breaker as the disconnect instead of a non-fusible switch.

What have you used or seen in the field. Any part #'s would be helpful.

shortcircuit
Top
Work Gear for Electricians and the Trades
#46870 - 01/04/05 07:04 PM Re: Building Disconnect
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
I don't think that you will find many non-fusible disconnects that are listed as service equipment.
Don
_________________________
Don(resqcapt19)
Top
#46871 - 01/05/05 06:31 AM Re: Building Disconnect
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Most of Square D's non-fusible 240V and 480V disconnects/safety switches are UL Listed as service entrance.

Square D does not make a knive blade design 2 pole non-fusible switch except as NEMA 3R 240V 30 & 60A sizes. So, it is likely that your supply house only stocks 3 pole devices.
Top
#46872 - 01/05/05 11:06 AM Re: Building Disconnect
velect Offline
Member
Registered: 05/01/04
Posts: 81
Loc: st joseph mi usa
A breaker disconnect would be a lot less expensive. Almost half the price
Top
#46873 - 01/05/05 05:07 PM Re: Building Disconnect
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
We sell the enclosed circuit breaker 3R for service disconnects. It is a lot less expensive. Smallest we sell is the 100 amp rated size. Just place a 60 amp 2-pole cb in it.
Top
#46874 - 01/06/05 05:59 AM Re: Building Disconnect
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
If there is a breaker at the source of the feeder and it's coming from another panel, it's a sub panel not service eqpt. Use any 3R disconnect.
Top
#46875 - 01/06/05 06:10 PM Re: Building Disconnect
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
I decided to get a Nema 3R circuit breaker enclosure suitable for service equipment for my accessory building disconnect which has a feeder run underground to it from a seperate building.

A knife style non-fusible disconnect suitable for service equipment was unavailable in the supply house.

I wanted to use a knife style disconnect outside the building because I envisioned that it would be easier for emergency personal to identify it as the building disconnect and it would be just a throw of a handle to shut down the building power.

Steve Miller...225.31 requires a disconnect and 225.36 says it must be suitable for service equipment.

thanx

shortcircuit
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals