#46834 - 01/03/05 06:09 PM Strange Happenings
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Did a panel replacement today and had a strange occurence which I am trying to understand. After reconnecting all the breakers and switching everything on, one 15 amp breaker would not hold. An ohmeter showed a tad over 8 ohms between this circuits hot wire and ground. Thinking there was a motor load or something I checked everything out and unplugged everything on the circuit. The 8 ohms remained. Then I happened to switch one of the 3 way switches for a stairway light. The 8 ohms went away. Switching the 3 way made it return. With the 3 way switched off, the breaker reset just fine. The stairway light works fine from both switching locations. It's a single, incandescent. Everything works fine now, but the breaker will not hold if you try to switch it on with the 3 way on. I should mention it is a multiwire circuit with the hots on opposing legs.
Anyone have any idea whats up here?
Top
Work Gear for Electricians and the Trades
#46835 - 01/03/05 06:22 PM Re: Strange Happenings
Coastal Offline
Member
Registered: 12/17/04
Posts: 23
Loc: Kill Devil Hills, NC 27948
Sounds as if the 3 way may be fed at both ends on the same phase??? Check the wiring between the switches to make sure it is correct; traveler not being used as common, etc.

[This message has been edited by Coastal (edited 01-03-2005).]

[This message has been edited by Coastal (edited 01-03-2005).]
Top
#46836 - 01/03/05 07:02 PM Re: Strange Happenings
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
I have seen switch legs brought into the panel and wirenutted into a branch circuit to control it. Panel basically being used as a J box. Had your same problem once with an oil burner emergency switch because of this. I assumed that the black& white was a branch circuit. Turn the switch on and the breaker tripped.

You should always be careful when taking the wiring apart in the old panel to note how everything is wired.

-Hal
_________________________
www.myphonetechs.com
Top
#46837 - 01/03/05 07:25 PM Re: Strange Happenings
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Hal,
I do take a good note of everything before I take it apart and label if neccesary. I've seen switch legs brought to the panel, in fact I did a pool light this way once after the original switch leg went bad under a slab.
There were no white wires anywhere but on the neutral/grd buss. Even the 240 loads were red and black. Take note where I said all works fine when hooked up, I just can't switch the breaker on with the 3 way on at the same time. Once the breaker is set, you can switch the 3 ways all day long with no problems.
I'm baffled.
I have another day to spend there, I will examine the 3 way wiring.
Coastal, I am having a hard time picturing your scenario. And why everything works fine once the breaker is set.


[This message has been edited by BigB (edited 01-03-2005).]
Top
#46838 - 01/04/05 06:13 AM Re: Strange Happenings
mvrandazzo Offline
Member
Registered: 05/13/02
Posts: 110
BigB,
This could be a loop fed circuit. I ran across this before. The original panel had a circuit fed from the panel on each end from two fuses. It was fed from the same side of the bus. When I changed the panel it was fed from opposite sides of the bus and tripped the breaker with no loads. Switch the offending breaked off and see if the terminal still has voltage. If it does then switch off the remaining breakers to see which circuit has the loop connection.
Hope this helps.

Blessings,
Mark Randazzo
Top
#46839 - 01/04/05 02:20 PM Re: Strange Happenings
gideonr Offline
Member
Registered: 12/18/04
Posts: 161
Loc: Edinburgh, Scotland, UK
Incandescent lamps have a very low resistance when cold, so draw a huge current at startup. The resistance rises as the filament warms up. But I'd have thought a breaker would cope with that anyway. Faulty breaker?
Top
#46840 - 01/05/05 12:19 AM Re: Strange Happenings
wirenut73 Offline
Member
Registered: 05/24/04
Posts: 27
Loc: Kansas City MO
It isn't on an AFCI by chance is it?
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals