#4669 - 10/09/01 06:58 PM circuit breaker trip time
spkjpr Offline
Member
Registered: 12/01/00
Posts: 218
Loc: Sedalia,MO, USA
I went on a troruble call today for a breaker tripping on an outdoor sign. The breaker did not slam like a direct short so upon amping I found that it will hold 60 amps for a couple of seconds. I know that a breaker will hold a large overload for a time due to inverse trip characteristics but could not find any tables in the NEC ( 99 version I believe, it's in the truck and too lazy to go check). I have seen some info on this but can't remember where I found it. Would like to know so I can better explain it to the customer other than , yep they'll hold for a while. Thanks guys.
Top
Work Gear for Electricians and the Trades
#4670 - 10/09/01 07:00 PM Re: circuit breaker trip time
spkjpr Offline
Member
Registered: 12/01/00
Posts: 218
Loc: Sedalia,MO, USA
Sorry,troruble should be trouble. Fingers move faster than the brain sometimes, really need to use spellcheck!!
Top
#4671 - 10/09/01 07:20 PM Re: circuit breaker trip time
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
You have to go to the breaker manufacturer for the trip curves. Many are on the web. What size, model and brand breaker are we talking about here?
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#4672 - 10/10/01 04:50 AM Re: circuit breaker trip time
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Ditto resqcapt. You need the info.
BTW,
I had to troubleshoot a sign fed by an underground conduit that tripped sometimes. When it did, the current rapidly(2-3 seconds) increased from 16-17 amps to 60,70,80,trip. The underground j-box had become exposed and, depending on the weather(dry, damp, or wet ), the breaker would either hold or not. It was interesting that once the current started to flow to ground, it started low, but rapidly increased to the point of tripping . Had to re-feed overhead.
Top
#4673 - 10/10/01 06:53 PM Re: circuit breaker trip time
spkjpr Offline
Member
Registered: 12/01/00
Posts: 218
Loc: Sedalia,MO, USA
Thanks, guys. And Redsy I'l check that out when I go back tomorrow.
Top
#4674 - 10/11/01 01:57 PM Re: circuit breaker trip time
WARREN1 Offline
Member
Registered: 05/09/01
Posts: 176
Loc: Greenville, SC, USA
Redsy
Was there a splice in the j-box?
We saw some good stuff from 3M for splicing in underground j-boxes and direct burial. Plan to spec it on our present project.
Top
#4675 - 10/11/01 06:50 PM Re: circuit breaker trip time
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Actually it was a rat's nest. Flush with grade in a used car lot, no cover, exposed wire ends, gravel & dirt filled. Amazed nobody got hurt. The box was so distorted that if I had a cover, it would never fit. Had to kill the whole thing & start over.
Top
#4676 - 10/19/01 11:05 AM Re: circuit breaker trip time
spkjpr Offline
Member
Registered: 12/01/00
Posts: 218
Loc: Sedalia,MO, USA
Found the trouble. The ballast sits in th e bottom of the sign annd had a large puddle around it. Replaced the ballast and set it up on a block so the water did not drown it.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals