#46515 - 12/24/04 01:59 PM Testing of Motors *** HELP***
acetoday Offline
Member
Registered: 09/18/03
Posts: 36
Loc: Manassas, Va
My customer has a pool pump (120v/5amps) which is relatively new (3 weeks old). Here is the problem, the customer without checking with me first ran 12-2 UF cable on the surface to keep the pool circulating through out the winter so the pipes wouldn't freeze. However, the pump is located approximately 225 ft from the main panel. The pump was plugged in for approx 2.5 weeks.

I calculated the vd at 2.25 volts which would require number 10 wire. Now when he plugs the pump in it kicks the breaker. This circuit is not on a GFCI protected. The customer did this without checking with me also.

Here is my question: Is there a way to check the leads on the motor for a direct short. I suspect the motor has burned out.
Top
Work Gear for Electricians and the Trades
#46516 - 12/24/04 02:04 PM Re: Testing of Motors *** HELP***
dryden_burton Offline
Member
Registered: 11/24/04
Posts: 11
Loc: Maple Creek, Saskatchewan, Can...
you could use a continuity tester or a multimeter put one lead one each conductor to see if there is a short.
_________________________
Dryden
Top
#46517 - 12/24/04 02:12 PM Re: Testing of Motors *** HELP***
russ m Offline
Member
Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
with the motor leads not tied to anything, You should'nt read anything on the meter from the wire to the case of the motor.
Put the tester across the two motor leads and you should read the resistance of the motor winding and not a short circuit.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:08 AM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
3 registered (Ruben Rocha, Admin, Fidellis), 132 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/07/00
Posts: 3190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals