#46472 - 12/23/04 01:52 PM Generator testing with bldg. load
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Apparently nursing homes are required to test thier standby generators by transfering the building load to the generator. Has anyone seen any problems associated with this monthly switch throwing??
(e.g. voltage spikes or dips)
Top
Work Gear for Electricians and the Trades
#46473 - 12/23/04 02:19 PM Re: Generator testing with bldg. load
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
It is more than a dip, it is an interruption.

You will want to make sure any items like PCs are either off or on UPS.

I don't believe you will see see spikes or other issues as the switch won't transfer until the generator is running smoothly.

I am assuming a modern automatic transfer switch.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#46474 - 12/23/04 04:04 PM Re: Generator testing with bldg. load
NJ Wireman Offline
Member
Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
we have a gen. system in our fire station that we test monthly, we kick it over with everything on pc tv's what ever happens to be on at the time. Never had a problem in 11 years. let me tell ya you hate to be the guy to test it when that thing throws itself its loud.

[This message has been edited by NJ Wireman (edited 12-23-2004).]
Top
#46475 - 12/23/04 04:12 PM Re: Generator testing with bldg. load
slumlordworker Offline
Member
Registered: 12/20/03
Posts: 88
Loc: south bend indiana
I worked as maintenance supervisor for over a year at a nursing home and I never had any problems with our generator.

we were required to run ours once a week and throw or trip the switch once a month. I rigged a meter up to the panel that it feed to get voltage measurements.

all was fine til we had an ice storm and that poor thing ran for about 9 hours than finaly it gave the ghost. talking about a erious issue when it is 25 outside and your healthcare provider has no power or heat at all that was a long and intresting night to say the least
Top
#46476 - 12/23/04 07:15 PM Re: Generator testing with bldg. load
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Many health care facilities specify a transfer switch that has the ability to sync and briefly parallel with the utility so there is no outage for the required testing.
Don
_________________________
Don(resqcapt19)
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 90 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 02/21/04
Posts: 1248

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals