The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
1 registered (Admin), 166 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#46467 - 12/22/04 03:42 PM Isolated ground outlets
nov Offline
Member

Registered: 08/08/04
Posts: 70
Loc: New Jersey
I need to install a couple of Iso. gnd. outlets. I was going to use 12/3 and attach the bare conductor to the box, the white to neutral, black to hot, and tape the red green and go to the outlet ground and tape the other end green at the panel for the ground bar. Is the correct? Also wanted to know what is the advantage to using the Iso. gnd. outlets.
thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#46468 - 12/22/04 05:20 PM Re: Isolated ground outlets
rlc3854 Offline
Member

Registered: 09/08/04
Posts: 14
Loc: Amite, LA
What the heck are you talking about, tape the red green etc. Where are you trying to install the isolated ground, residential, commerical or industrial. What is the voltage and what type of panelboard/load center to you have. If this is residential and the ground and grounded conductor are bonded you can not do what you want without seperating the ground and grounded conductor. Heavy electronics used to require isolated grounds but todays thinking has changed depending on heavy motor loads and harmonics.

Top
#46469 - 12/22/04 05:32 PM Re: Isolated ground outlets
hbiss Offline
Member

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
What is the advantage of an isolated ground receptacle? In most cases none.

You can re-identify the red as the iso ground however you need to consider a few points and what that isolated ground conductor is going to do for you.

First, both receptacles should be individual home runs or at least the isolated grounds need to be run individually back to the panel from each receptacle.

Second, in your case, instead of going to all that trouble just use plastic boxes, a regular receptacle and 12/2 NM home runs from each receptacle back to the panel. You now have your isolated ground without all the agravation.

-Hal

[This message has been edited by hbiss (edited 12-22-2004).]
_________________________
www.myphonetechs.com

Top
#46470 - 12/22/04 07:17 PM Re: Isolated ground outlets
Sandro Offline
Member

Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
Plastic boxes in commercial work? eeesh. It's available in Canada and it's code for us too now, we must use a proper 12-3 BX wire with the black, white, and green coloured conductor along with a bare ground. Taped red's are no longer acceptable!

Top
#46471 - 12/22/04 10:19 PM Re: Isolated ground outlets
ComputerWizKid Offline
Member

Registered: 09/20/03
Posts: 116
Loc: Connecticut, USA
Can you instand them without an isolated ground? I like the orange color outlets
_________________________