The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (geoff in UK), 213 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#45993 - 12/09/04 06:41 PM Strange new local code
arseegee Offline

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Today I had the pleasure(?) of sitting through a three hour meeting with the big wigs of the home builders association and several other sub-contractors reviewing a list of codes that will be enforced in my local jurisdiction.

The problem is we have three county inspectors and all of them have different opinions on grounding, bonding, smoke detectors and so forth. Structural issues are also hit or miss when it comes to notching and boring.

Well I'm going through the list and 95% of the codes agree with the NEC but a new bonding requirement made no sense to me.

The new bonding rule will be to bond the "hot" and cold copper water pipes to the service at the water heater. Now this is new to me and I would like some opinions on this issue.

We bond cold water lines but never the hot. I was under the impression that dielectric unions were used on water heaters to keep the lines from pitting. Any info would be greatly appreciated!

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#45994 - 12/09/04 07:00 PM Re: Strange new local code
HotLine1 Offline


Registered: 04/03/02
Posts: 6791
Loc: Brick, NJ USA
We have been bonding the H&C water pipes at the water heaters for quite a while.

Reason: The pipe entry points are plasticlined, therefore no mechanical metalic bond on the "hot" water piping.

This applies to elec and gas HW htrs, and is required on a service upgrade, or replacement of elec water heaters. Logic is a permit is required for an electric water heater, so the EC has to bond; gas water heaters require a plumbing permit, and the plumbers cannot do EC work.

I can't give you an article, my stuff is in the twp car.

Take care & Happy Holidays.


#45995 - 12/09/04 07:00 PM Re: Strange new local code
mustangelectric Offline

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Metal water or gas pipes and BUILDING STEEL...IF THEY EXIST...Shall be bonded to the GEC.

You should also be bonding the motor case of spas or whirlpool tubs to a #8 solid to any copper lines around the spa and water meter too.

The handbook shows a bond around the water meter and then to building steel.

HW supply line makes sense, it is COPPER.

I do not see any problem there myself. What is the concern?



[This message has been edited by mustangelectric (edited 12-09-2004).]
Electricity has no respect for ignorance!

#45996 - 12/09/04 07:04 PM Re: Strange new local code
NJ Wireman Offline

Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
We bond it in Jersey have been for awhile, building steel,water feed jumping water meter ands hot water heaters above there valves.

#45997 - 12/09/04 07:12 PM Re: Strange new local code
arseegee Offline

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Thanks for the replies guys. It's old dog - new tricks i guess. I am just use to only bonding the cold in the five other jurisdictions we work in.

I know art 250 requires all metal piping to be bonded but was under the ASSumption that the hot was not to be bonded. But we all know about assumptions.

And yes we bond whirlpool motors too, but all the resi water meters are fed by PVC then PVC to the house.


#45998 - 12/09/04 07:34 PM Re: Strange new local code
Electric Eagle Offline

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Ron, Up here in North Georgia, we've been doing this for years. I'm surprised you haven't already been doing this. How've you been doing? You haven't been around much any more. Didn't you have back surgery?

#45999 - 12/09/04 08:00 PM Re: Strange new local code
arseegee Offline

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Hi David, yeah I quess were behind the times here. As for me, my back surgery went fine. I have to be careful as to what I do but I'd say I am 95%. I have been busy this year, not so much with the biz (which has been off some... bummer) but I built a new house and had my first child last month. A little girl who will be my office manager one

How has your year been? I fell behind on my commercial bids while building my house but it's been nice to have some time with my wife and child. I'll be slammed here in a few weeks though. We have dozens of new houses coming out of the ground to go on top of the 20 we have going right now and I got the bid on 25 convenience stores and 40K sqft of retail space. So if you get caught up, gimme a call!

Take care, and I am so sorry Ga Southern didn't woop up on the Dawgs earlier this year... just kidding.

[This message has been edited by arseegee (edited 12-09-2004).]

#46000 - 12/10/04 11:55 AM Re: Strange new local code
jbfan Offline

Registered: 02/21/03
Posts: 75
Loc: Newnan, GA
I'm sorry they didn't woop up on them either.

"Yes I am a Pirate, 200 years to late" Jimmy Buffett

#46001 - 12/15/04 06:05 PM Re: Strange new local code
sgreany Offline

Registered: 07/18/03
Posts: 25
Make perfect sense to me. Would a jumper simular to a water meter jumper work?

#46002 - 12/17/04 06:50 AM Re: Strange new local code
sabrown Offline

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
As for pitting in the water lines, that is typically caused where the water heaters coating on the core has been compromised (by age and electrolisys (spelling?) typically in an electric water heater where anode replacement was not kept up). The iron particles from the deteriating water heater then migrate into the copper water lines where gravity pulls them to the bottom of the pipes when waterr is not flowing. The iron comes in contact with the copper (dissimilar metals) and causes the pitting.