#4597 - 10/05/01 04:45 AM hot ground on switch
ken m Offline
Member
Registered: 08/14/01
Posts: 61
Loc: south carolina
anyone have ideas regarding the best way to locate a possible drywall fastener that has penetrated an nm cable? i would imagine that to be the problem. with the ground wire connected to a light switch people are getting the 'buzz'. thx for any help. ken m
Top
Work Gear for Electricians and the Trades
#4598 - 10/05/01 06:01 AM Re: hot ground on switch
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Ken,

What do you mean by "getting the 'buzz'" ?

Bill
Top
#4599 - 10/05/01 10:47 AM Re: hot ground on switch
ken m Offline
Member
Registered: 08/14/01
Posts: 61
Loc: south carolina
bill, just hick talk for getting shocked when touching the cover screws. i did find the problem. a poor wiring job to begin with because the equip gnd was snipped off the supply cable. the gnd wire in the 14/3 feeding the light/fan combo from the switch was terminated on the switch gnd screw and and the fan housing with a potential of 120v. found that the nm cable clamp had been overtightned to a point of mashing not only the nm sheath but the wire insulation of the ungrounded wire as well to a point of contact between the hot wire and the clamp.
not sure why they went to the trouble of grounding the fan and switch and omitting the main equipt gnd cond from the source.
Top
#4600 - 10/05/01 02:31 PM Re: hot ground on switch
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
ken,

Gotcha!
It seems like the 14/3 that is made now cannot take tightening of the Rx clamps. The dimple probably digs into it. I always try to give a few wraps of tape around the cable before tightening the clamp.

Bill
Top
#4601 - 10/05/01 03:19 PM Re: hot ground on switch
pauluk Offline
Member
Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
At least you have clamps on boxes for Romex.

The equivalent cables here are just run through a knock-out with a rubber grommet so there's nothing to actually clamp the cable firmly. It should be clipped close to the box, but frequently isn't, so strained connections inside are quite common if someone's tugged at the loose cable.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 123 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals