The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 192 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#45761 - 12/06/04 06:11 PM Knob and Tube wiring
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Got a call to replace a couple of lights in a little ole ladys house ...so I went to look at what she wants hung and the place was old, with K&N wiring still.

Am I supposed to upgrade the wiring to the ceiling outlet when hanging new light fixtures??

Not sure if the little ole lady can afford to rewire the house to hang a few new lights??

shortcircuit

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#45762 - 12/06/04 06:22 PM Re: Knob and Tube wiring
detubbs Offline
Member

Registered: 11/18/04
Posts: 52
Loc: PA
can't ya just run a new circuit for the light instead of rewiring the whole house??
_________________________
Scott

Top
#45763 - 12/06/04 06:44 PM Re: Knob and Tube wiring
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
I don't think you have to rewire to hang the light anymore with knob and tube, than you would if it were wired with the old style bx that does'nt have the ground strip in it. It was code compliant when it was installed and I don't think you are altering it.

Top
#45764 - 12/06/04 06:52 PM Re: Knob and Tube wiring
Electric Ian Offline
Member

Registered: 02/10/04
Posts: 132
Loc: MA, USA
I would think that you could replace the lighting fixtures without having to replace the existing knob and tube wiring based on
80.9(B)
In fact, 394.10 allows installation of knob and tube as an extension to an existing circuit.
I don't believe that existing knob and tube in hollow spaces of walls and ceiling constitutes an "imminent danger to occupants". Buried in insulation though - well, that's a differant story.

Top
#45765 - 12/07/04 03:06 AM Re: Knob and Tube wiring
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Most new lights I've installed say wiring must be rated 90 degrees.

When I've droped an old over bulbed fixture connected to knob and tube in the past...the wires insulation is so dryed out it crumbles and falls off if you move it at all.

Also I've found that most of a floor will be wired on 1 or 2 circuits at best...so if you kill one lighting circuit it may require rewiring many lighting outlets.

Also does'nt article 250 say I must ground the newly installed fixture?

What is your experiance with Knob and Tube???

shortcircuit

Top
#45766 - 12/07/04 12:46 PM Re: Knob and Tube wiring
Steve McKinney Offline
Member

Registered: 04/30/04
Posts: 80
Loc: Marion, Illinois
Shortcircuit............If it is accessible from the attic, I try to pull it up and run the K&T into a non-metallic j box. Hopefully you have some "Loom" left to run each wire into the knockouts. The loom is the flex tube over the wire, I have been told. One wire per ko. Then tie in some good stuff to it. As long as you are 8' away from grounded appliances, I believe you will be ok. IMHO

Steve

Top
#45767 - 12/07/04 04:17 PM Re: Knob and Tube wiring
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
You should install a cut-in (old-work) J box behind your new fixture. And, both the box and the fixture should be non-metallic, as there is no equipment ground. A nice keyless lampholder wih a clip on shade would fit the bill. But, they do make plastic fixtures that look nice, too.
By the way, they still make and sell loom for covering the conductors of K & T wiring.
_________________________
Earl