The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#45728 - 12/05/04 06:11 PM 2000 watt movie lamp trips GFCI
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
I have a customer who's brother is in the filming business. He has a 2000 Watt lamp that he says trips the GFCI every time he powers it up. The filming area is all GFCI protected. The best explanation I can come up is the high inrush from the cold tungsten filament must be causing an imbalance between the line/neutral enough to trip the GFCI. I suggested using a dimmer to bring the lamp up slower.Am I even on the right track?
Top
Work Gear for Electricians and the Trades
#45729 - 12/05/04 07:03 PM Re: 2000 watt movie lamp trips GFCI
RobbieD Offline
Member
Registered: 02/23/03
Posts: 238
Loc: Canada
Is it a gfci breaker or receptacle? What is the rating of the breaker?
Top
#45730 - 12/05/04 07:06 PM Re: 2000 watt movie lamp trips GFCI
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
It's a GFCI receptacle, 20 amp on a 20 amp ckt with downline receps on it's load side. The light works fine on a non GFCI 20 amp circuit. I thought at first maybe a ground/neutral fault in the fixture, then I thought about the inrush.
Top
#45731 - 12/05/04 07:15 PM Re: 2000 watt movie lamp trips GFCI
RobbieD Offline
Member
Registered: 02/23/03
Posts: 238
Loc: Canada
Well I know that some reactive circuits trip GFI's but if this is a total resistive circuit it should work fine. Is it a total resistive circuit? 16.6 A is high for that circuit anyway. But if its only on now and then it should be fine.

[This message has been edited by RobbieD (edited 12-05-2004).]
Top
#45732 - 12/06/04 04:08 PM Re: 2000 watt movie lamp trips GFCI
cpalm1 Offline
Member
Registered: 01/06/04
Posts: 62
if the light MUST be GFCI protected, and there are nobody else can think of a better idea, then try using a dimmer switch on the light. make sure it has a 2000 watt capacity. with the dimmer you could bring the bulb up to full power slowly, reducing the inrush.
Top
#45733 - 12/06/04 04:35 PM Re: 2000 watt movie lamp trips GFCI
GA76JW Offline
Member
Registered: 03/20/04
Posts: 195
Loc: Suwanee, GA USA
Quote:
16.6 A is high for that circuit anyway


Coming from the one 2000 watt lamp alone you have the 16.6 Amps, With basic ohm's law. let alone what else is on the circuit. It's probably a good chance it is overloaded.
_________________________
"If common sense was common, everyone would have it"-not sure, someone here

Top
#45734 - 12/06/04 05:18 PM Re: 2000 watt movie lamp trips GFCI
smokumchevy Offline
Member
Registered: 02/14/03
Posts: 62
Loc: Ottawa, Ontario, Canada
Can you not just use a GFCI class 'B' instead to prevent nuisance tripping in this case?

-Greg
Top
#45735 - 12/06/04 07:01 PM Re: 2000 watt movie lamp trips GFCI
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
"Coming from the one 2000 watt lamp alone you have the 16.6 Amps, With basic ohm's law. let alone what else is on the circuit. It's probably a good chance it is overloaded."

I thought it was a misconception that a GFCI receptacle will trip on overload. I thought it would only trip on ground fault.

I think I will ask him to let me check out the lamp, just to satisfy my curiosity.
Top
#45736 - 12/06/04 07:14 PM Re: 2000 watt movie lamp trips GFCI
RobbieD Offline
Member
Registered: 02/23/03
Posts: 238
Loc: Canada
Your right GFCI receptacles do not trip on overcurrent.
Top
#45737 - 12/07/04 10:32 AM Re: 2000 watt movie lamp trips GFCI
hbiss Offline
Member
Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Why are GFCI receptacles being used there anyway? This a kitchen show? I'm for using GFI's where required but if you use them everywhere because you are paranoid you are going to have problems like this.

-Hal
_________________________
www.myphonetechs.com
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 123 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals