The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 220 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#4559 - 10/02/01 07:09 AM GFI Wiring Drawing - Discussion Hosted By Nick
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Discussion thread for Schematic drawing posted for ECN's Member "Nick" in the Technical Reference Area under the subject heading:

GFI Wiring Schematic - Per ECN Member

Please feel free to ask questions, or make comments for Nick, in regards to this drawing.

Scott SET. 10/02/2001 07:07:00

Edit= embedded hyperlink to schematic

[This message has been edited by Scott35 (edited 10-02-2001).]
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#4560 - 10/04/01 07:58 PM Re: GFI Wiring Drawing - Discussion Hosted By Nick
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Just to add a little explanation to this one. This is a Modified Differential Ground fault system designed by GE Industrial systems for a specific project. It is just an example of how to tie together multiple services and feeds that all have, and are required to have, ground fault protection.
This one has three 4000A services (utility feeds) tied together with tie breakers. In addition to the services there are two 1500KVA generators paralleled and tied directly to one of the sub station bus via a kirk-key system. All 5 sources have ground fault protection and require neutral to ground bonds for it to operate. Not code legal you say? (I sure did at first) Well it works by forcing the neutral current to the appropriate breaker (the one in use) so it's ground fault circuitry senses properly.
It is NEC compliant if approved by the AHJ and apparently is not uncommon where multiple services are utilized.

Top
#4561 - 10/05/01 03:32 AM Re: GFI Wiring Drawing - Discussion Hosted By Nick
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Pretty fancy Nick,
those kir-key systems are quite the alternative to a T-switch, are there any links to read/view etc. about them that U know of?

Top
#4562 - 10/05/01 10:59 PM Re: GFI Wiring Drawing - Discussion Hosted By Nick
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
If your looking for info on Kirk Keys check out
www.kirkkey.com

Top
#4563 - 10/06/01 12:42 AM Re: GFI Wiring Drawing - Discussion Hosted By Nick
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Very neat work Nick!
I think We should start a directory somewhere to catalog these things.
I'll put it on the 'to do' list


Bill