It's really clear situation for me with 110/230 voltage system. But on one canadian factory I meet 347/575 v. Usually to get 120 we use a transformer. So question is how the factory get this 575 V and 347 V. Thanx
Top
Work Gear for Electricians and the Trades
#45540 - 12/01/04 03:43 PM Re: 347 and 575 voltage ?
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
The same way you guys get 480V and 277V.

347V is one phase of a 600V wye to ground.


edit - sorry, I thought this was from US poster. 120V/240V is found on a single phase system. 120V/208V is found on 3 phase system. 347V/600V also found on 3 phase system. With 600V coming into the premises, a xfmr is still needed to get 120V.

[This message has been edited by Sandro (edited 12-01-2004).]

[This message has been edited by Sandro (edited 12-01-2004).]
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals