ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 17
Recent Posts
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,479 Are you busy
166,185 Re: Forum
160,639 Need opinion
Who's Online Now
1 registered members (geoff in UK), 47 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#45321 - 11/23/04 08:23 PM Low voltage door contacts  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 812
NC
The alarm job I talked about earlier is kind of giving me an education. I endeavored to upgrade an existing alarm type system, which had a 120 volt a/c to 15 vdc converter, that fed normally opened door contacts, then fed back to an alarm. The door contacts were broke and I replaced them, plus added other door contacts throughout the facility, and also added 2 more 12 vdc sirens and 1 more internal alarm. Since this didn't go through a control panel, the full load of the alarms went through the contacts. I didn't realize how much of a load was going through the contacts, until I mounted one of the last ones before fininshing the job, or so I thought [Linked Image] The last door contact welded itself together when I tested the alarm again. Hopefully I can remedy this situation, by going through the door switches, then letting the return wire energize a 12 vdc relay, and breaking the main 12 vdc through the contacts on the relay, thus allowing the load to flow through the contacts on the relay, instead of the contacts on the door. The contacts on the relay are rated 7.5 amps, and I will only be pulling 4 amps on 15vdc. The coil itself only pulls 1.5 watts verses the 60 watts that the contacts were loaded to. Is there anyone with any other suggestions, to my dilema here. Wonder if I'm missing something about this set up I'm thinking about doing? Any thoughts would be appreciated. Thanks.. Steve


Work Gear for Electricians and the Trades

#45322 - 11/24/04 06:21 AM Re: Low voltage door contacts  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
That would be a very unusual set-up with the contacts just operating the alarm directly. The norm would be for a relay (or these days an equivalent electronic circuit) which serves a dual purpose: 1. Keeps the current in the contacts down, as you describe, and 2. Provides a method for the alarm to latch on.

With the contacts operating the alarm directly, anyone opening a door and hearing the alarm start only has to close it again to stop it.

If you just want a basic latching relay circuit, use a relay with double-pole normally-open contacts. Wire one pair in parallel with the door contacts and use the other pair to operate the alarms. Then when the alarm is triggered, the relay latches on via its own contacts and the alarm will continue until turned off.

The more common arrangement is for door/window contacts to be normally closed and wired in series so that any break in the circuit triggers the alarm.



Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7429 MB (Peak: 0.8577 MB) Zlib enabled. Server Time: 2017-03-26 09:17:35 UTC