The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 216 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#45074 - 11/18/04 04:31 PM Rotary Phase Converter???
acetoday Offline

Registered: 09/18/03
Posts: 36
Loc: Manassas, Va
I need to install a rotary phase converter tomarrow and haven't had time to research as much as I had wanted. If anyone can help it would be greatly appreciated.

Here are the specs:

Runs 220V three phase equipment (In this case an ice cream maker) from a 220v single phase source. The motor is 3 H.P. I'll be installing it approx 30ft from main panel to a 3 phased disconnect then to the phase converter.

My question is what size wire should I use for the branch circuit conductors and what size breaker at the panel? I had already run #12 Romex assuming a single phase 220v load protected by a 2-pole 20. However, the customer got a good deal on a 3 phase ice cream maker. I'm not sure if #12 will still be OK.

Again, any comments would be greatly appreciated.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#45075 - 11/18/04 06:10 PM Re: Rotary Phase Converter???
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
You will have to identify what the nameplate states for minimum circuit amps, and max breaker size, then work from there. If it says #12 is ok, then it's ok. It will probably have a 30 or 35A max breaker size.