#44975 - 11/16/04 10:10 AM Readily Accessible Fuel
Dave55 Offline
Member
Registered: 05/08/04
Posts: 697
Loc: Crystal Lake, Illinois, USA
I looked at a garage where the guy wanted me to move a welder outlet. It's next to a sub-panel (with holes) from the house. Leaning up against the sub-panel is some cardboard, and on the floor against the cardboard are two cans with gasoline.

After moving the cardboard and gasoline away from the panel I go in the house to see how the sub-panel is fed. I find a 40-amp, 240-volt breaker double-tapped with two 12-3 w/ground UF cables.

I guess his thinking was that if 12 ga. is good for 20-amps, then two of them are good for 40-amps. I told him if he had ten on the breaker it should still only be a 20-amp breaker. To top it off, the white wires were unused, with the bare ground going from neutral bar to neutral bar. No grounding in the detached garage, of course. I told him I'd have to fix the over-fuse before doing anything with the welder outlet and he wasn't interested.

I'm starting to give serious thought to charging the "diagnostics fee" that other contractors charge.

Dave

Spelling

[This message has been edited by Dave55 (edited 11-16-2004).]
Top
Work Gear for Electricians and the Trades

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals