can someone here tell me what the abbrev "HACR" stands for on Sq D breakers. (for use w/ heating and refer equip., having motor group combinations, and marked for use with HACR curcuit breakers.)...so far I looked in articles 240, 404, 440, and the index. just want to know what the abbrev spelled out is.
thanks.
Top
Work Gear for Electricians and the Trades
#44964 - 11/16/04 09:51 AM Re: HACR type
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Heating Air conditioning and refrigeration
_________________________
Ryan Jackson,
Salt Lake City
Top
#44965 - 11/16/04 10:31 AM Re: HACR type
goodwill Offline
Member
Registered: 08/23/04
Posts: 54
Loc: Madison, WI, USA
thanks Ryan!
Top
#44966 - 11/16/04 12:46 PM Re: HACR type
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
This trade uses a lot of acronyms. I went for about three years before I finally asked someone what it stood for (I didn't want to look like an idiot). Waiting that long was the stupid part. That is the nice thing about forums like this, you ask a question and get (normally) an answer without anyone laughing at you.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#44967 - 11/16/04 02:33 PM Re: HACR type
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Your certainly welcome.

While we're on this topic, perhaps someone can give me an answer to this:

I have been told that any molded case circuit breaker listed under the UL 429 (I think 429???) for overcurrent devices already meets all of the requirements for an HACR device. I beleive there is something in article 430 of the 2005 that addresses this as well.

Does anyone have any input on that?
_________________________
Ryan Jackson,
Salt Lake City
Top
#44968 - 11/16/04 02:51 PM Re: HACR type
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Edit to above: UL 489
_________________________
Ryan Jackson,
Salt Lake City
Top
#44969 - 11/16/04 02:57 PM Re: HACR type
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
Ryan, I found this in the UL White Book but didn't find anything in the 2005 NEC.
Quote:
Circuit breakers investigated for use with heating, air conditioning and refrigeration equipment comprising multi-motor or combination loads are marked ‘‘HACR TYPE,’’ in conjunction with the Listing Mark. Such circuit breakers are suitable for use with heating, air conditioning and refrigerating
equipment marked for use with HACR type circuit breakers. Use of these circuit breakers with heating, air conditioning and refrigerating equipment is limited to installations where the equipment is marked as suitable for use with any properly sized circuit breaker, or is marked for use with a HACR type circuit breaker, or is not limited by any marking as to the type of branch circuit, short-circuit and ground-fault protective device.
This was found under CIRCUIT BREAKERS, MOLDED-CASE AND
CIRCUIT BREAKER ENCLOSURES (DIVQ).
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#44970 - 11/16/04 04:41 PM Re: HACR type
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Charlie, does that mean I can no longer use HACR breakers for everything under the sun, spare SWD (switch duty breakers)?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#44971 - 11/16/04 05:57 PM Re: HACR type
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
I don't believe you ever could.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#44972 - 11/17/04 08:45 AM Re: HACR type
goodwill Offline
Member
Registered: 08/23/04
Posts: 54
Loc: Madison, WI, USA
CharlieE,
that's what actually got this thread started for me. the facility I work at now swapped out a bunch of panels in 2 of our buildings a few years ago, and within the last year, about 40 two-pole breakers "froze up" in the off/tripped position. Upon replacement of said breakers, it was discovered that they were of the HACR type. I had a hunch that they wore out due to misapplication. (they were feeding lights and outlets.) either that, or they just got a bad batch off the production line?
>Will
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (Admin), 60 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals