The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 184 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#44383 - 11/02/04 08:49 PM Underground Long PVC Run
InspectorE Offline
Member

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
I have a long run (1300') of PVC for some decorative lighting along a driveway. The lamps will be spaced about 130' apart. I'm wondering what the experience is regarding expansion/contraction of the PVC conduit. I know the temp down at 4' or so is pretty constant, but at 2' I'm not so sure it's constant. I certainly don't want any fittings to pull apart. Above ground, expansion fittings would be mandatory.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#44384 - 11/03/04 09:16 AM Re: Underground Long PVC Run
goodwill Offline
Member

Registered: 08/23/04
Posts: 53
Loc: Madison, WI, USA
InspectorE,
300.5(J) ground movement,
and 300.7(B) expansion fittings.
I'm assuming that you are in a zone 3 or 4.(did a google on "frost zones")
I personally probably would not bother with the expansion fittings if you can get down to 48"...like you said, it should stay a constant 55┬░
anything less than 4', I would put one every 50-100'. 352.44(A) (let's say in the summer the earth is an even 55┬░, and in the winter it is 32┬░., so 1.01 inches per 100'.)

Top
#44385 - 11/03/04 04:00 PM Re: Underground Long PVC Run
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
for conduit that is buried, you will not have to be concerned about expansion fittings.

Pierre
_________________________
Pierre Belarge

Top
#44386 - 11/03/04 07:12 PM Re: Underground Long PVC Run
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Check Carlon literature, UG is OK without exp. joints. But, you must be stubbing 'up' at the fixture locations, No??

You may get ground heaving conditions by/at the stubs.

BTW, if you have concern, I do not know of any prohibition (NEC) or mfg that says you cannot install exp joints if you want.

John
_________________________
John

Top
#44387 - 11/03/04 08:07 PM Re: Underground Long PVC Run
InspectorE Offline
Member

Registered: 10/08/04
Posts: 51
Loc: Hudson WI USA
There will be lantern posts (5' high or so?) every 130'. Since it is underground, it has to be wet rated wire, so I'm not too concerned about any leakage/condensation inside the conduit. Stubs will have to be brought up to the posts, that's correct. Fortunately, the lamps are only 25 w or so, the voltage drop won't be a big factor.