The open delta thread brought this question to mind.

Is it wise to land one leg of a double pole breakers on the B phase for common loads such as water heaters, motors or HID lighting as long as your breaker has a 240 volt rating?

Or are double poles only rated in slash ratings?
Top
Work Gear for Electricians and the Trades
#44145 - 10/28/04 07:12 PM Re: Delta & 1Ph Load
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
No. The voltage furnished by the electric utility is 120/240 volts, 3 phase, 4 wire and does not include the 208 volts that you are wanting to use. If you use it, the voltage is sometimes a bit screwy and we don't care about that voltage. Some electric utilities even prohibit loads being connected in that manner.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#44146 - 10/28/04 07:41 PM Re: Delta & 1Ph Load
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
huh?

what if the voltage you are looking for is 240V, then a 2-pole breaker on A & B phase would be 240V. What is the problem with that? I am not sure I follow. Charlie, are you talking about using a single pole breaker on the high phase ("wild leg") that is prohibitted?

I would say it wise to use a 2-pole breaker that way, it leaves you more 120V spaces open for your single pole breakers.
Top
#44147 - 10/28/04 07:58 PM Re: Delta & 1Ph Load
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
If you have a corner grounded delta and have a two pole breaker that lands on phase B, it must be straight rated (240) and not slash rated (120/240).

This is due to the fact that a ground fault on phase A or phase C is 120 volt, but a ground fault on phase B is 208, which is in excess of the individual pole rating of the slash rated breaker. See 240.85

To answer the second part of the question, no, not all 2 pole breakers are straight rated. In fact, most are not. Last time I saw, a straight rated breaker costes about 5 times as much as a slash rated.
_________________________
Ryan Jackson,
Salt Lake City
Top
#44148 - 10/28/04 08:38 PM Re: Delta & 1Ph Load
arseegee Offline
Member
Registered: 01/28/02
Posts: 324
Loc: Statesboro, GA USA
Thanks for the replies.
Top
#44149 - 10/29/04 03:45 AM Re: Delta & 1Ph Load
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
I misunderstood the question. You know, that is the first mistake I have made this year.

I thought the question was to go from the grounded conductor to the high phase with the circuit to get 208 volts and that is the way I answered it. Sorry.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#44150 - 10/29/04 04:56 AM Re: Delta & 1Ph Load
Jps1006 Offline
Member
Registered: 01/22/04
Posts: 615
Loc: Northern IL
Ryan, are sure that's how the slash rating is to be read, I have always understood the slash rating to expand the use of these breakers, not limit them. Where can I find more info about slash rating, and why is a single pole QO slash rated? (as I type MW branch circuit comes to mind.)

Also a phase to phase short would be a 240V short with a more likely lower impedance path. How is it a breaker could be designed to handle that, yet somehow a lower voltage and likely lower energy fault to ground be beyond the breaker's capacity and rating?

no sweat Charlie, at that pace it should be your only mistake this year.

[This message has been edited by Jps1006 (edited 10-29-2004).]
Top
#44151 - 10/29/04 05:18 AM Re: Delta & 1Ph Load
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
Ryan's correct for circuits that include the B phase, read 240.85. Of course the single phase circuits that only use the A and C phases can use the slash rated circuit breakers since they are using just a single phase transformer. Since we serve a lot of residential customers with open delta banks (we use the three phase to serve a small business that is next to the residential area), the residential customers would all have to use full rated circuit breakers if that wasn't permitted.

By the way,
Quote:
Charlie, are you talking about using a single pole breaker on the high phase ("wild leg") that is prohibited?
I would be interested in the reference in the Code that prohibits that installation, I have never been able to find the reference.

- - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#44152 - 10/29/04 05:23 AM Re: Delta & 1Ph Load
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
The single poles are rated that way because of people who use two of them to obtain 240v.
Top
#44153 - 10/29/04 06:03 AM Re: Delta & 1Ph Load
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Jps: If you have a minute, download this presentation from Bussmann. It is about 2.5 Megabytes, but is well worth it, even if you have a dial up connection. You might want to right click the link and select "save target".

http://www.bussmann.com/services/training/docs/240-85Pres.ppt
_________________________
Ryan Jackson,
Salt Lake City
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals