The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#44144 - 10/28/04 07:03 PM Delta & 1Ph Load
arseegee Offline
Member

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
The open delta thread brought this question to mind.

Is it wise to land one leg of a double pole breakers on the B phase for common loads such as water heaters, motors or HID lighting as long as your breaker has a 240 volt rating?

Or are double poles only rated in slash ratings?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#44145 - 10/28/04 07:12 PM Re: Delta & 1Ph Load
CharlieE Offline
Member

Registered: 04/23/04
Posts: 204
Loc: Indianapolis
No. The voltage furnished by the electric utility is 120/240 volts, 3 phase, 4 wire and does not include the 208 volts that you are wanting to use. If you use it, the voltage is sometimes a bit screwy and we don't care about that voltage. Some electric utilities even prohibit loads being connected in that manner.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy

Top
#44146 - 10/28/04 07:41 PM Re: Delta & 1Ph Load
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
huh?

what if the voltage you are looking for is 240V, then a 2-pole breaker on A & B phase would be 240V. What is the problem with that? I am not sure I follow. Charlie, are you talking about using a single pole breaker on the high phase ("wild leg") that is prohibitted?

I would say it wise to use a 2-pole breaker that way, it leaves you more 120V spaces open for your single pole breakers.

Top
#44147 - 10/28/04 07:58 PM Re: Delta & 1Ph Load
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
If you have a corner grounded delta and have a two pole breaker that lands on phase B, it must be straight rated (240) and not slash rated (120/240).

This is due to the fact that a ground fault on phase A or phase C is 120 volt, but a ground fault on phase B is 208, which is in excess of the individual pole rating of the slash rated breaker. See 240.85

To answer the second part of the question, no, not all 2 pole breakers are straight rated. In fact, most are not. Last time I saw, a straight rated breaker costes about 5 times as much as a slash rated.
_________________________
Ryan Jackson,
Salt Lake City

Top
#44148 - 10/28/04 08:38 PM Re: Delta & 1Ph Load
arseegee Offline
Member

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Thanks for the replies.

Top
#44149 - 10/29/04 03:45 AM Re: Delta & 1Ph Load
CharlieE Offline
Member

Registered: 04/23/04
Posts: 204
Loc: Indianapolis
I misunderstood the question. You know, that is the first mistake I have made this year.

I thought the question was to go from the grounded conductor to the high phase with the circuit to get 208 volts and that is the way I answered it. Sorry.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy

Top
#44150 - 10/29/04 04:56 AM Re: Delta & 1Ph Load
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
Ryan, are sure that's how the slash rating is to be read, I have always understood the slash rating to expand the use of these breakers, not limit them. Where can I find more info about slash rating, and why is a single pole QO slash rated? (as I type MW branch circuit comes to mind.)

Also a phase to phase short would be a 240V short with a more likely lower impedance path. How is it a breaker could be designed to handle that, yet somehow a lower voltage and likely lower energy fault to ground be beyond the breaker's capacity and rating?

no sweat Charlie, at that pace it should be your only mistake this year.

[This message has been edited by Jps1006 (edited 10-29-2004).]

Top
#44151 - 10/29/04 05:18 AM Re: Delta & 1Ph Load
CharlieE Offline
Member

Registered: 04/23/04
Posts: 204
Loc: Indianapolis
Ryan's correct for circuits that include the B phase, read 240.85. Of course the single phase circuits that only use the A and C phases can use the slash rated circuit breakers since they are using just a single phase transformer. Since we serve a lot of residential customers with open delta banks (we use the three phase to serve a small business that is next to the residential area), the residential customers would all have to use full rated circuit breakers if that wasn't permitted.

By the way,
 Quote:
Charlie, are you talking about using a single pole breaker on the high phase ("wild leg") that is prohibited?
I would be interested in the reference in the Code that prohibits that installation, I have never been able to find the reference.

- - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy

Top
#44152 - 10/29/04 05:23 AM Re: Delta & 1Ph Load
watthead Offline
Member

Registered: 10/13/01
Posts: 182
Loc: South Carolina
The single poles are rated that way because of people who use two of them to obtain 240v.

Top
#44153 - 10/29/04 06:03 AM Re: Delta & 1Ph Load
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Jps: If you have a minute, download this presentation from Bussmann. It is about 2.5 Megabytes, but is well worth it, even if you have a dial up connection. You might want to right click the link and select "save target".

http://www.bussmann.com/services/training/docs/240-85Pres.ppt
_________________________
Ryan Jackson,
Salt Lake City