#44070 - 10/27/04 07:01 AM riser
velect Offline
Member
Registered: 05/01/04
Posts: 81
Loc: st joseph mi usa
I have to raise a ten foot 2-1/2 IMC riser about three feet. Building is going from a flat roof to a trussed one.
Can I use a 3 foot piece of PVC between the meter base and the 10 foot IMC without bonding issues
Top
Work Gear for Electricians and the Trades
#44071 - 10/27/04 08:40 AM Re: riser
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
No.
_________________________
John
Top
#44072 - 10/27/04 02:57 PM Re: riser
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
how did you get your 8 ft above the flat roof if you don't have the clearance over the trussed roof? you would be isolating the IMC from the grounding in the meter base.
Top
#44073 - 10/27/04 03:35 PM Re: riser
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
You could bond the riser at the top end to the neutral if you want.

Personally I would only extend this with the same type of raceway.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#44074 - 10/27/04 04:16 PM Re: riser
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
I know around here you can't use anything for mast except steel RMC. Even though it isn't part of the immediate load bearing portion of the service entrance, I'd think it would still be subject to torsion from wind, etc, and I'd use IMC like the original section.

Check with your AHJ, but they'll probably insist on the use of IMC.
Top
#44075 - 10/28/04 04:49 PM Re: riser
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
Don't leave out the serving electric utility since it will be their service cable that will be hitting the service mast. If it doesn't meet their requirements, you may not get hooked up.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals