The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (NORCAL, sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#43613 - 10/16/04 08:28 PM GFCI receptacles and Inspectors
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
I had a situation with the county deputy inspector this week. He was doing a final on a new house I had wired and informed me that all of the GFCI receptacles would have to be replaced so he could re-test them before he would sign off on the final electrical. I asked what the problem was and he told me that when he tested them with his Ideal receptacle tester they would trip okay but upon being reset they didn't register as hot. These are P&S Safelock 15A GFCI receptacles. He demonstrated for me and it was just as he said. I asked him to unplug his tester before he reset the GFCI. When he did this the power was restored to th GFCI immediately. The inspector thought these were all faulty GFCI receptacles(12 in this home)and wanted them replaced. I referred him to the manufacturer's instructions which state the GFCI receptacle should be tested using the test button on the receptacle. The instructions also refer to the device meeting the 2003 UL requirements. I wonder if the Safelock feature requires anything plugged into the receptacle at the time it trips to be unplugged before power is restored to the receptacles. The info that comes with the GFCI doesn't mention it. The GFCI would reset with the tester still plugged in, it just wasn't "hot" until he unplugged the tester and then plugged it back in. Anyone else run in to this? By the way, he passed all of them after repeating his test unplugging the tester after tripping and reset.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#43614 - 10/16/04 08:42 PM Re: GFCI receptacles and Inspectors
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
I can't be of any help to you, but I certainly appreciate the "heads up" on the receptacles.

Top
#43615 - 10/16/04 08:47 PM Re: GFCI receptacles and Inspectors
Jacuzzi Guy Electric Offline
Member

Registered: 10/25/02
Posts: 33
Loc: Dearborn Heights Michigan Unit...
This is normal on the Receptacles. They are new and the "lock" feature is for this purpuse. The inspector has NOT been informed... I think. Check out this funny Movie. http://www.elec-toolbox.com/Pics/funny%20electricity%20joke%20guy%20plays%20on%20friend.mpg Or download direct at http://www.elec-toolbox.com/Pics/elecpics.htm

Top
#43616 - 10/17/04 12:49 AM Re: GFCI receptacles and Inspectors
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
 Quote:
The GFCI would reset with the tester still plugged in, it just wasn't "hot" until he unplugged the tester and then plugged it back in.


Maybe it was the tester that would not register as hot, maybe he has not learned to use his new toy? Try it again with a simple GFCI tester.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#43617 - 10/17/04 06:13 AM Re: GFCI receptacles and Inspectors
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
I did try it with a simple tester and it produced the same results. I also plugged my Fluke T5 600 in the top of the GFCI while he plugged his tester in the bottom to monitor voltage while he tested. Same thing, no voltage upon reset until he unplugged his tester.

Top
#43618 - 10/17/04 10:01 AM Re: GFCI receptacles and Inspectors
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Thats interesting Fred, thanks for posting it.

When I inspect, I put my tester in, trip the device then pull out the tester and use the ground pin on my tester to reset the device, so I've never ran into that.

Good info to know though.
_________________________
Ryan Jackson,
Salt Lake City

Top
#43619 - 10/19/04 07:29 PM Re: GFCI receptacles and Inspectors
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
I have seen it where I would test a GFI with my little tester, then I would go to rest it and the "Open Ground" light would come on and it looked like a bad GFI. I would then trip it again with the GFI's tester button, and reset it once more. Then averything would act normal. I have seen these several times in the past year in many different house. It seems you have to test and restet twice before it resets properly. Just my 2 cents. By the way,, I have seen a gfi, tried to test it with my tester and nothing happened. I would then check the test button and it would work. So My gFI tester went bad. So now I carry 2 GFI testers just in case.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals