#43339 - 10/10/04 08:38 PM And this building passed inspection ???
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
Yesterday I looked at a building that was being remodeled in a WV city that has electrical inspectors.The new service was hot so it was inspected .With casual observation I found the following NEC violations.
1.BX with no antishort bushings
2.Bonding screw installed in panel beond disconnect.
3.No equipment ground bus in panel.
4.No cold water ground.
5.10'of greenfield in 2" conduit run to new panel with no bonding around greenfield.
6.Equipment grounds tied to neutral.
7.Equipment ground conductor from outside service disconnect is under the neutral lug in the panel.
8.Feeder to rental unit supplied from panel in main building.
9.No bonding bushings on 2"conduit feeding new panel.
It is nice to live in a state that qualified electrical inspectors.
Top
Work Gear for Electricians and the Trades

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals