#43328 - 10/10/04 07:13 PM nuetral question
rj Offline
Member
Registered: 01/23/03
Posts: 21
Loc: Skidmore, Missouri, USA
This might be a dum question and it mighthave been asked before, but here goes. Why does the nuetral always seem to burn? Me and the guys I work with have all wondered why this happens. Thanks for any information that you can give me.
Top
Work Gear for Electricians and the Trades
#43329 - 10/10/04 07:18 PM Re: nuetral question
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
First thing that comes to mind is unbalanced load. Second, the old edison wiring method on 3-ph systems where they shared 3 hots of a, b & c phase and used one nuetral.
Top
#43330 - 10/10/04 07:44 PM Re: nuetral question
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
the same thing with multicircuit single phase also when someone is not too bright with L-N-L set up and when the load get uneven it will actally over heat too and once a while i will see the diy's do put the breaker on wrong leg and end up burn the netural wire pretty bad i did see it happend few places it is no fun to fix it right


merci, marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#43331 - 10/10/04 11:09 PM Re: nuetral question
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Quote:
First thing that comes to mind is unbalanced load.

I'd second that!.
Neutrals in 3 phase wye systems carry the (usually minimal) out-of-balance current and unless there is a gross imbalance of the loads, shouldn't usually be a problem.
However, one situation where I have seen a Neutral get so hot the PVC insulation melted off it, was where an Electrician used a Neutral that was only half the size that it should have been, in a 3wire 230 system over here.

[This message has been edited by Trumpy (edited 10-11-2004).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#43332 - 10/11/04 03:17 AM Re: nuetral question
SteveMc Offline
Member
Registered: 02/05/04
Posts: 62
Loc: Rock Hill, SC
Computers and other non-linear loads add to neutral overheating. any circuit that will have a lot of electronics need it own neutral. The other problem that I have found is loose connections at the neutral bar due to more than one wire under the screw.
Top
#43333 - 10/11/04 07:49 AM Re: nuetral question
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Quote:
Computers and other non-linear loads add to neutral overheating.

Only on three phase wye systems. The neutral problem with nonlinear loads does not happen on single phase 120/240 volt three wire systems.
Don
_________________________
Don(resqcapt19)
Top
#43334 - 10/11/04 07:12 PM Re: nuetral question
Norstarr Offline
Member
Registered: 09/25/04
Posts: 86
Loc: Wi
You will usually find this situation when someone has relocated breakers in a panel and now have both circuits on a three wire circuit on the same leg in the panel. Instead of the neutral carrying the difference between the two circuits now it is additive. If you have two 20 amp breakers the neutral could concievably carry 40 amps, hence the burnt or discolored neutral wire. And as Stevemc stated, it is caused by loose connections at the neutral bar. I make it a habit that whenever I open a customers panel I tighten all connections. Takes a minute and if they are there it leaves an impression.
Ron
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals