The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#43295 - 10/08/04 09:41 AM Feeder Problems Looking for Answers
cvictory Offline
Junior Member

Registered: 10/08/04
Posts: 2
Loc: ok
I have a 480 3ph step down transformer feeding a 120/240v panel twenty feet away.
The feeders are 4 - 4/0 with ground. The panel is suppling electronic games and has a full 42 circuits in it with seperate nuetral for each branch circuit. The problem is the nuetral feeder is pulling 250amps and is warm to the touch. The phase conductors in the feeder are pulling 180 to 190 amps and are hot to the touch. Any ideas on why the phase conductors are hotter than the nuetral and how to fix?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#43296 - 10/08/04 09:55 AM Re: Feeder Problems Looking for Answers
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Of course just a guess, but ..........

triplen harmonics.
_________________________
Ron

Top
#43297 - 10/08/04 10:59 AM Re: Feeder Problems Looking for Answers
cvictory Offline
Junior Member

Registered: 10/08/04
Posts: 2
Loc: ok
Well I knew it had to do with harmonics but the thing about it is that I would of thought the nuetral would of showed more rise in temperature than the phase conductors. I know the code says to upsize the nuetral in this situation and that sometimes the nuetral may end up larger than the phase conductors. But I would of figured there to be a higher temperature on the nuetral since the amperage is higher.
Thanks

Top
#43298 - 10/08/04 02:59 PM Re: Feeder Problems Looking for Answers
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
hi,
it sounds like you are exceeding the permissible load on the branch circuits..

4/0 and a 190 A load? does that not send up a flag for you?

arent you seeing inductive heating..the more heat the higher the resistance..

i would up the size of the service..and feeders to reduce the load below 80%..
it also sounds like you have an unbalanced load..and some shared neutral issues..

-regards


mustang
_________________________
Electricity has no respect for ignorance!

Top
#43299 - 10/08/04 03:42 PM Re: Feeder Problems Looking for Answers
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
neutral feeder is pulling 250amps and is warm to the touch. The phase conductors in the feeder are pulling 180 to 190 amps and are hot to the touch. Any ideas on why the phase conductors are hotter than the nuetral and how to fix?


Possibly loose connections of the ungrounded conductors to the panel lugs or lugs to panel.

You did not say the panel rating or if the 4/0 is AL or CU.

To me what you described sounds like a 75 KVA transformer feeding a 225 amp panel with 4/0 copper.

If I assumed wrong disregard the following.

If that is the case 180 amps is the highest allowed continuous load for this panel. The transformer would be rated 208 amps.

There is only one way to fix this and that is reduce the load.

You could run a second 4/0 neutral and try to order a 200% rated neutral bar for this panel to deal with the high current on the neutral.

After doing this you will still have an overloaded panel. The transformer will also still be dealing with 250 amps on the neutral. Ron or Dereck could say if this will shorten the transformer life.

BTW, I hope these are copper conductors.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#43300 - 10/08/04 04:04 PM Re: Feeder Problems Looking for Answers
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
I haven't dealt with harmonics on a neutral. Please post your findings here.

If the phase conductors feed into a main breaker in the panel, the heat could be coming from the breaker.

I had a harmonic problem that was tripping a breaker. Every year the molded case breaker had to be replaced. The customer's decision was that it was cheaper to suffer down time and replace breakers every year than to install a harmonic filter. It was on an oil well, so I assume that the harmonic correction was very expensive.

Top
#43301 - 10/09/04 10:56 AM Re: Feeder Problems Looking for Answers
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
cvictory — The description sounds more like it may be 208Y/120V service from the 480-primary transformer. Is that the case?

A low-end IR non-contact thermometer may be more "accurate" than fingers.

Top
#43302 - 10/09/04 11:51 AM Re: Feeder Problems Looking for Answers
big guy Offline
Member

Registered: 12/19/03
Posts: 52
Loc: pa
did you check the grounding in the transformer?
is there any equip. that is burning up?

Top
#43303 - 10/10/04 12:48 PM Re: Feeder Problems Looking for Answers
dereckbc Offline
Member

Registered: 10/08/03
Posts: 158
Loc: Tulsa, OK
I would like to comment, but something is not clear too me.

"I have a 480 3ph step down transformer feeding a 120/240v panel twenty feet away".

Huh? Can you clarify? Do you have a 480 delta primary with 208/120 output? Or do you have a 480 input, 240/120 output. I can understand the high neutral current on a 208/120 system, but not on a 240/120 system.

Please clarify. Need to know size, type, and "K" rating of transformer. Normally for this type of installation you would use a delta 480 input, 208/120 output, "K-13" rated step-down transformer, and a panel with 200% neutral bus bar.