The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 248 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#43035 - 10/02/04 05:55 AM Arc Welder - Voltage Reduction
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
An arc welder rated 230V 3Ph.,70A. was transferred from one of our facilities to another. The new location has a building electrical system of 120/208V. 3Ph. 4W.
We would like to spare the expense of boost transformers if possible. Will the 230 volt rated arc welder operate adequately if fed with 208 volts?

[This message has been edited by Frank Cinker (edited 10-02-2004).]

[This message has been edited by Frank Cinker (edited 10-02-2004).]

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#43036 - 10/02/04 10:33 AM Re: Arc Welder - Voltage Reduction
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I've put welders on 120/208 systems several times with no problem. The operator usually has to crank up the amps one or two settings above what he is normally used to using. Since most welding operations do not max out the amps, you should be OK. However, if the users usually run near the top end, you may have to install the transformers..

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#43037 - 10/02/04 05:15 PM Re: Arc Welder - Voltage Reduction
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
 
Generally, where voltage changes over a fixed resistance, power output changes with the square of voltage ratio. So… (200/230)² ≈ (208/240)² ≈ 0.75 or a power-output reduction of 25%.




[This message has been edited by Bjarney (edited 10-03-2004).]

Top
#43038 - 10/02/04 05:17 PM Re: Arc Welder - Voltage Reduction
Ray97502 Offline
Member

Registered: 10/02/04
Posts: 55
Loc: Central Point,OR
I have never done such a thing but I would expext that it is possible. However you would need insure that the branch circuit was sized sufficently tho handle the additional current. It would not be 125% of 70A and I'm not sure if the calculation would be 125% 77A (230/208*70) or 121A (1.73*70). When you consider the additional power (I sqrd R) loss over time (depending on the amount of use this welder will have) it may be cheaper to buy a boost xfmr.

Top
#43039 - 10/03/04 06:10 AM Re: Arc Welder - Voltage Reduction
Mike Wescoatt Offline
Member

Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah
Almost all of our welders (TIG, MIG, Stick) as well as one of our plasma cutters are made for 230V. We run them at 208 with no problems. More and more you'll find today inverter machines that will accept anything from 208v 1Ø to 480v 3Ø without changing any of the taps. If you have taps for 200v, use those. Lastly, if your machines are CC/CV sources then it really shouldn't matter except on the top end of the machine since they'll compensate for the reduced input by raising their output accordingly.
_________________________
Mike Wescoatt

Top
#43040 - 10/04/04 09:10 AM Re: Arc Welder - Voltage Reduction
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
 
Mike, thank you for bringing us into the modern world of switchmode power supplies for something besides PCs, like “lunchbox” welders nowadays.

Indeed — http://www.millerwelds.com/pdf/spec_sheets/DC29-5.pdf "The Auto-Line circuitry automatically connects to 120—460VAC, single- or three-phase power…"

My ancient 60% duty-cycle Airco box has 200-230-460V straps [and old, large but very inefficient selenium rectifiers and a 'mag-amp' saturable reactor for current control.]




[This message has been edited by Bjarney (edited 10-04-2004).]

Top
#43041 - 10/04/04 06:34 PM Re: Arc Welder - Voltage Reduction
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
Your machine will be around long after the newer equipment is long gone.........

Top
#43042 - 10/04/04 11:56 PM Re: Arc Welder - Voltage Reduction
Big Jim Offline
Member

Registered: 07/18/03
Posts: 377
Loc: Denver, CO USA
Bjarney,
Your's sounds a bit like mine but mine is a big mamma - 100% duty cycle up thru 200 amps, rated over 400 amps on TIG.
These new 'inverter' welders are slick and portable but I don't think and of them will ever run DC as smooth as mine which has a 200 pound inductor in series in the output line. At moderate amps, the welding sounds more like a whoosh that the crackle you always hear about. At about 1000 pounds, it just isn't very portable.

Top
#43043 - 10/05/04 09:15 AM Re: Arc Welder - Voltage Reduction
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Jim, I lied. It's a Linde box {arch comepetior to Airco.}

[Doesn't every guy carry a picture of their welder in their wallet? And nowadays, jpegs on their computer?]