#42993 - 09/30/04 08:59 PM is this a fair statement?
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
A built in microwave if draws more than 50% of the circuit breakers rating then that circuit should not have other loads on it.

If this statment is true would you please find a code reference that would back-up my statement.

I know this rule applies to window A/C units but can not find a NEC section that applies to kitchen appliances such as a built-in microwave.

Thanks a bunch
Edward
_________________________
Thanks
Edward
Top
Work Gear for Electricians and the Trades
#42994 - 10/01/04 07:23 AM Re: is this a fair statement?
sparky806 Offline
Member
Registered: 12/07/02
Posts: 59
Loc: Shawnee, KS, USA
210.3(2)
Top
#42995 - 10/01/04 08:02 AM Re: is this a fair statement?
Edward Offline
Member
Registered: 12/14/02
Posts: 308
Loc: California
Thank you for the reply.


Edward
_________________________
Thanks
Edward
Top
#42996 - 10/01/04 12:47 PM Re: is this a fair statement?
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
Is the micro a built in if not it is not fastened in place. I think 210.23 (A) (1) may be applicable

(1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
Manufactures generally do not install 15 A cord connectors for utilization equipment which operates in excess of 12 A., 16 A for a 20A cord connector etc.(80%)


(2) Utilization Equipment Fastened in Place, addresses specifically that equipment which is fastened in place, such as built in units. It's intent as I read it is to limit that equipments load to not more than 50% of the branch circuit capacity if other cord connected equipment may use the same branch circuit. Most BI Micros will require a individual Branch circuit and the receptacle that is installed in such cases should be a single contact device.

Hope that helps

Charlie


[This message has been edited by cpal (edited 10-01-2004).]
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 74 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals