#42938 - 09/28/04 09:07 PM Home Alarm Troubleshooting
Mty Jerry Offline
Junior Member
Registered: 09/28/04
Posts: 2
Loc: Monterey, CA, USA
I have installed a DSC PC1555 hard wire alarm system with a PC 1575 LED keypad after checking all wiring and allowing the back battery to fully charge I tried to get the system to operate. The "trouble" light appears with zone light 1 on which indicates "Service Required" I would like to know what needs to be done to allow the system to operate properly. No other lights come on indicating all other systems are working properly. Any assistance would be greatly appreciated.
Thanks Mty Jerry
Top
Work Gear for Electricians and the Trades
#42939 - 09/29/04 06:46 AM Re: Home Alarm Troubleshooting
rmiell Offline
Member
Registered: 11/09/00
Posts: 242
Loc: La Junta, Co. USA
Does this system need an end-of-line resistor installed?

Have you tried the company's tech support?

Good luck.

Rick Miell
Top
#42940 - 09/29/04 07:11 AM Re: Home Alarm Troubleshooting
WESTUPLACE Offline
Member
Registered: 03/29/04
Posts: 251
Loc: Kingwood, TX USA
All zones must have EOL resistors installed including the fire zone. If not, you will have a trouble light. Also if the comunicator has been programmed and the phone line is not connected it will also show trouble.
Top
#42941 - 09/29/04 03:00 PM Re: Home Alarm Troubleshooting
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
also ohm the zones at the panel for grounds, and the zone in question, ohm the pair and verify that you can " see" the EOL on the zone.
Top
#42942 - 09/29/04 05:51 PM Re: Home Alarm Troubleshooting
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Here is what you do :

Approach the keypad. Press * 2 The Zone that lights up indicates the trouble. If its Zone 1, then press "1" again. If its one of the other Zones see the chart :

Here are the Zone codes :

Zone 1 - Service Required

light 1) low battery
light 2) bell circuit trouble
light 3) general system trouble
light 4) general system tamper
light 5) general system supervisory
light 6) not used

Zone 2) AC failure
Zone 3) Telephone Line Monitoring
Zone 4) Failure to communicate
Zone 5) Zone Fault
Zone 6) Zone Tamper
Zone 7) Device Low Battery (if you are using wireless)
Zone 8) Loss of system time.

I am willing to bet you have 2 troubles. I think its the loss of system time. You must program the time in the system to work properly. And, I think you have TLM trouble. The manual explains how to disable the TLM, OR, run a phone line to the system so that it "see's" a dial tone.

End of line resisters are optional for this system. It can be disabled through programming if EOLs have NOT been used.

Please let me know how you make out.
Top
#42943 - 09/29/04 06:57 PM Re: Home Alarm Troubleshooting
Mty Jerry Offline
Junior Member
Registered: 09/28/04
Posts: 2
Loc: Monterey, CA, USA
I have programed it for the time, date, etc. I will try to diaable the TLM as you suggest. I do have the phone connected and checked to make sure it was working properly.
Thanks Jerry
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals