#42793 - 09/26/04 08:07 AM High Voltage Terminations With Dieless Crimpers
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
I work with a group that if it is newer than 1940 technology it just will not work. Or so they believe. 2 years ago we bought a Burndy Y644M Dieless crimper they seem to like it on 480 volt work they were not sure about it at first but they did come around. They absolutly refuse to use it on 2400 and 13.2KV work. Their argument is that it makes a triangular shaped crimp with rounded corners and indented base it would create uneven stress around the lug or butt splice and cause the splice or termination to fail.I talked to the Burndy rep and he said their conserns are unwaranted.What is your all experinces with dieless crimpers on HV work. THANKS HYPRESS
Top
Work Gear for Electricians and the Trades
#42794 - 09/26/04 08:31 AM Re: High Voltage Terminations With Dieless Crimpers
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Hypress,
All I can say is:
Absolute bunkum!.
Provided that you are only using that sort of crimp on Copper conductors, I can't see a problem.
We've used this sort of crimp profile here for years in New Zealand and in some cases, it's more reliable than Hex-Crimp profiles.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#42795 - 09/26/04 09:19 AM Re: High Voltage Terminations With Dieless Crimpers
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
We use that tool for 5 and 15 kv terminations all the time with no problems. I do take the precaution of filling the indent with semiconductor tape before intalling the stress cone.
Don
_________________________
Don(resqcapt19)
Top
#42796 - 09/26/04 09:55 AM Re: High Voltage Terminations With Dieless Crimpers
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
I've never used anything else and it regularly passes a hi-pot test.
Top
#42797 - 09/26/04 07:50 PM Re: High Voltage Terminations With Dieless Crimpers
ComputerWizKid Offline
Member
Registered: 09/20/03
Posts: 119
Loc: Connecticut, USA
Whats HIPOT mean? I see it on all of my computer parts?
_________________________
Theres always enough room in the junction box.You just need a bigger hammer
Top
#42798 - 09/26/04 08:07 PM Re: High Voltage Terminations With Dieless Crimpers
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
The term HI-POT is a slang term for high potential testing of elecrtical wiring and equipment. Itis generally done with several thousand volts. There are standards you go by for new equipment and old equipment. It is generally done with DC however there AC HI-POTS.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 95 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals