The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (crselectric, mbhydro), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#42793 - 09/26/04 08:07 AM High Voltage Terminations With Dieless Crimpers
hypress Offline
Member

Registered: 07/20/04
Posts: 132
Loc: Charleston WV
I work with a group that if it is newer than 1940 technology it just will not work. Or so they believe. 2 years ago we bought a Burndy Y644M Dieless crimper they seem to like it on 480 volt work they were not sure about it at first but they did come around. They absolutly refuse to use it on 2400 and 13.2KV work. Their argument is that it makes a triangular shaped crimp with rounded corners and indented base it would create uneven stress around the lug or butt splice and cause the splice or termination to fail.I talked to the Burndy rep and he said their conserns are unwaranted.What is your all experinces with dieless crimpers on HV work. THANKS HYPRESS

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#42794 - 09/26/04 08:31 AM Re: High Voltage Terminations With Dieless Crimpers
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Hypress,
All I can say is:
Absolute bunkum!.
Provided that you are only using that sort of crimp on Copper conductors, I can't see a problem.
We've used this sort of crimp profile here for years in New Zealand and in some cases, it's more reliable than Hex-Crimp profiles.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#42795 - 09/26/04 09:19 AM Re: High Voltage Terminations With Dieless Crimpers
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
We use that tool for 5 and 15 kv terminations all the time with no problems. I do take the precaution of filling the indent with semiconductor tape before intalling the stress cone.
Don
_________________________
Don(resqcapt19)

Top
#42796 - 09/26/04 09:55 AM Re: High Voltage Terminations With Dieless Crimpers
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
I've never used anything else and it regularly passes a hi-pot test.

Top
#42797 - 09/26/04 07:50 PM Re: High Voltage Terminations With Dieless Crimpers
ComputerWizKid Offline
Member

Registered: 09/20/03
Posts: 116
Loc: Connecticut, USA
Whats HIPOT mean? I see it on all of my computer parts?
_________________________
Theres always enough room in the junction box.You just need a bigger hammer

Top
#42798 - 09/26/04 08:07 PM Re: High Voltage Terminations With Dieless Crimpers
hypress Offline
Member

Registered: 07/20/04
Posts: 132
Loc: Charleston WV
The term HI-POT is a slang term for high potential testing of elecrtical wiring and equipment. Itis generally done with several thousand volts. There are standards you go by for new equipment and old equipment. It is generally done with DC however there AC HI-POTS.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals