The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
51 minutes 32 seconds ago
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
0 registered (), 259 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#42701 - 09/24/04 06:02 PM Boiler Wiring
CRM Offline

Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
At work today, I had to rewire 4 heating system boilers in a commercial building. Three of these boilers had to run off of one thermostat, I was going to use a 3 pole control relay to accomplish this. Each of these boilers has it's own 24volt control circuit, a (R) and a (W) terminal to fire the boiler. The previous installer didn't use a relay, he joined all 3 (R) terminals together and all 3 (W) terminals together, from each boiler and put them on 1 thermostat. My thinking has always been, if you join 3 separate control systems together you would short them out, possibly burning out the transformers, but these boilers have worked like this for about a year. Is it okay to do this without a relay. Thanks for any replies.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#42702 - 09/24/04 06:55 PM Re: Boiler Wiring
twh Offline

Registered: 03/11/04
Posts: 895
Loc: Regina, Sask.
Nothing direct, but I talked to an electrician about that, this week. She told me that they must be on the same phase - something about the interconnected wiring between units. Sorry, but I didn't ask more questions. I'm a little slow before 10 cups of coffee.

#42703 - 09/24/04 07:03 PM Re: Boiler Wiring
leespark Offline

Registered: 01/17/04
Posts: 54
Loc: Massachusetts
It may work but it is not the way to do it IMO. Transformers do weird things when they "talk" to each other like that. It could also burn up the t-stat. I do quite a bit of heating-cooling wiring and always keep a couple of "RIB"s (relay in a box) in the truck. Constantly getting me out of a jam (about $12 each).

#42704 - 09/24/04 07:48 PM Re: Boiler Wiring
twh Offline

Registered: 03/11/04
Posts: 895
Loc: Regina, Sask.
leespark, I'll ask when I see her again, but I got the impression that it was manufacturer's specs. I agree with you, and she clearly agreed with us, but the manufacturer wins. It didn't work, then, when changed, it did work.

I'll ask.

#42705 - 09/25/04 11:09 AM Re: Boiler Wiring
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
“Jumpering” three control systems with individual control-power transformers through a single contact is very shortsighted—likely unreliable at very least—worse, unpredictably hazardous for boiler-operational safety.

It could very well be that the boilers are not shutting down by the subject thermoset, but instead being repeatedly cycled by safety-limit controls—which may be a very serious error.

[This message has been edited by Bjarney (edited 09-25-2004).]

#42706 - 09/25/04 11:38 AM Re: Boiler Wiring
Norstarr Offline

Registered: 09/25/04
Posts: 89
Loc: Wi
I feel they were very fortunate not to have had a problem on the control circuits of those boilers for such a long time. I agree with you regarding installing a three pole relay controlled by the thermostat. It looks more professional and should one boilers control circuit fail it would still allow the other ones to continue instead of dropping all three.

#42707 - 09/25/04 02:09 PM Re: Boiler Wiring
cpal Offline

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
If I'm following you correctly you are suggesting that the 24V power supplies are interconnected. I have not seen that for some time. What Class power supply are you working with? I would check 725.41 (B) Interconnection of Power Sources. Class 2 or Class 3 power sources shall not have the output connections paralleled or otherwise interconnected unless listed for such interconnection.
In my experience parallel systems are unreliable and subject to failure also as mentioned by previous posts.

#42708 - 10/10/04 08:47 PM Re: Boiler Wiring
twh Offline

Registered: 03/11/04
Posts: 895
Loc: Regina, Sask.
I did follow up on this. My friend's situation was two furnaces running off one stat. The manufacturer's specs were that they were to be fed from the same phase. Two interconnected furnaces, one stat, and approved that way. Sometimes we just have to be good little soldiers and, like it or not, do what we're told.