#42382 - 09/20/04 05:17 AM Panelboard Under Water
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Several of our Municipal firehouses have panelboards under water. After the water recedes what is the common procedure for restoring power?
After wiping off the busbars etc. of mud and drying with cloth, I'm considering placing a large floor stand fan in front of it to expedite the drying process.
Any other ideas?
Top
Work Gear for Electricians and the Trades
#42383 - 09/20/04 07:37 AM Re: Panelboard Under Water
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Frank:
Your intentions sound "good", BUT in my opinion you are asking for trouble down the road.

Common practice in this area is to replace any electrical equipment that has been in contact with flood waters. (Some large switchgear is the exception, pending FACTORY authorization)

Floodwaters contain a wide varitey of substances (toxic and otherwise) that can result in 'problems' after the fact. There's another thread around on a forum that has a link, or two to NEMA info.

John
_________________________
John
Top
#42384 - 09/20/04 09:10 AM Re: Panelboard Under Water
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Here is a link to information from Square D concerning flood damage. They say miniature (panelboard/loadcenter) breakers must be replaced.

[This message has been edited by JBD (edited 09-20-2004).]
Top
#42385 - 09/20/04 09:57 AM Re: Panelboard Under Water
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Very good information. Thank you!
Top
#42386 - 09/20/04 02:19 PM Re: Panelboard Under Water
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
Nema has guidelines for water damaged equipment. www.nema.org/papers/waterdam.html

you can download it and use this to help sell your project to the consumer.

Pierre
_________________________
Pierre Belarge
Top
#42387 - 09/20/04 03:39 PM Re: Panelboard Under Water
MONOLITH Offline
Member
Registered: 01/04/03
Posts: 45
Loc: Pennsylvania, USA
Replacing the equipment is the right thing to do.

Not only is it the proper thing for the consumer, but you don't make much money just drying it out for them.

After the rainy remains of Hurricane Frances came through Pennsylvania this weekend, I've been changing panels all over the place.
_________________________
www.MONOLITHELECTRIC.com
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals